Any Non sparks done the 2391 course ?? | Page 5 | on ElectriciansForums

Discuss Any Non sparks done the 2391 course ?? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Hi Spartykus I fully understand that but surely the T/s Spark would get some decent benefits in return i do have a decent skill set in IT and perhaps he has a wee office he needs pat testing that i could do as a favour for him .
I do make a lovely cup of Coffee and have a clean drivers licence and when told to tidy up dont bitch n moan like the average bairn would.
I respect my elders n betters and scrub up tidy for clean jobs :)

72-van

come on fife sparls where r u ?
 
Hi mate its possible to do if you put the effort in it isnt easy but possible as i had no experience of three phase inspection and testing before hand but i studied every day for 4 month its no walk in the park you have been given some good advice on revision
the books that have been suggested will help a lot focus mainly on the
GN3 as about 80% of exam based on this
then
Electricity at work regs 1989
GS38
another good book is Cristopher kitchers guide to inspection and testing its only about £11 and worth every penny explains it in a easier manner than the other books i have read
this the link to the book on amazon
Practical Guide to Inspection, Testing and Certification of Electrical Installations: Conforms to 17th Edition IEE Wiring Regulations BS 7671:2008 and Part P of Building Regulations: Amazon.co.uk: Christopher Kitcher: Books
practice loads of past papers as some of the questions crop up again and again plus it will give you a feel of how the C&G want it answered

they especially dont like incorrect terminology
learn all about the different test procedures and how to explain in bullet points
can be done with drawings as shown in gn3 or without also sometimes your asked for calculations as part of the answer
practice calculations for resistance and volt drop
the exam success is a good help keep practising with it until you can get a higher mark as possible without looking at the answers it will also give you a feel of the time taken for each question
Earth fault loop diagrams for all systems , TT, TN-C-S, TN-S, IT fully labelled with correct terminology
your course will show you a lot of this so practice in between the weekly lessons so its second nature
practice inspecting and testing as you have been advised on your system using safe isolation
there are loads of threads on the forum covering the 2391
a good one is the section 301 thread which is a sticky in the general section by Amberleaf his time and effort in posting this info i found a great help as there are sample questions etc in there
dont be afraid of asking mate thats what the forum is for
Good luck to you
 
Last edited:
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
Thank you Brucelee
I will order the book you suggest and get my nose into that one as well perhaps i am forunate that i dont know the incorrect termonologies that you mention and only those given to me in the 17th ed.
Also as you suggest i will have a good read of the forums postings on 2391 maybe best done after i read through the basics though :)

72-van
fife
 
Hi All Eventually got a tester on ebay today A metrel 61557 out of calibration so it will need sent off that .Hopefully here before the course starts next week so that i can have a read of the books you guys have recommended and a 'play' with the meter.

Next question am i right in thinking that i need a proving unit and a padlock type device for the practical course work ?

thx 72-van
 
Proving unit is not strictly necessary - on a job you can usually use live tails before the main switch for proving at a CU, but don't necessarily rely on this for assessment at college - they like it to be by the book. Proving units can be very expensive for what they are- if you were baulking at buying some of the books recommended to you, you will definitely find it hard to stump up for a proving unit. But then the college should have them available for use. And lock-off kits, unless you get a truly universal one, do not fit on all types of switches/breakers. So be aware of this when buying your lock-off kit. May be worth getting one just to suit your own equipment at home for practice until you can see what will be needed at college, though the college should be able to provide you with a lock-off kit suitable for their equipment.
 
Thanks Ringer
I've had a bid on a couple of proving units on the bay they seem to hold there money well .The c unit i have at home is quite old with re-wireable fuses so no use for any of the test rigs i had a look at the college as far as the lock mechs go.
Any brand of these universal lock kits in particular i should look at?
When i did the 17th they said they failed a guy on the 2391 for not locking the wotsit and keeping the key with him.

cheers 72-van
 
Thanks Ringer
I've had a bid on a couple of proving units on the bay they seem to hold there money well .The c unit i have at home is quite old with re-wireable fuses so no use for any of the test rigs i had a look at the college as far as the lock mechs go.
Any brand of these universal lock kits in particular i should look at?
When i did the 17th they said they failed a guy on the 2391 for not locking the wotsit and keeping the key with him.

cheers 72-van


Hi 72-van

it's got some credance still the 2391-10 because it's hard. So when you've got it it counts for something.

It heartens me when I hear that they're still failing people and acting all uptight about using the right phrases. Good!
 
Hi All Eventually got a tester on ebay today A metrel 61557 out of calibration so it will need sent off that .Hopefully here before the course starts next week so that i can have a read of the books you guys have recommended and a 'play' with the meter.

Next question am i right in thinking that i need a proving unit and a padlock type device for the practical course work ?

thx 72-van

college i did it at provided any testing kit needed. I used my own though -bit more reassuring to use something you are familiar with. Start using that tester on your own house and get the book that brucelee mentioned by kitcher. A real big help with the photos that it has.

You do need to get a look at a 3 phase board before the exam practical - it's not difficult once someone has explained it, just a bit different.
With determination you can do it. :)
 
Thanks Pushrod The three phase board has been mentioned to me a couple of times now and i will make 100% sure that i get the differences twixt this and a single phase board well in my head quite often on the 17th ed course one of the t/s sparks would explain something to me during a break which i didnt quite catch as indeed i was able to do for others when i did the 2377 course as i had years of practical exp of pat on it equipment.
I am confident that the guys on the course will be a little sympathetic to someone wanting to learn as the guys on this forum have been

its a great forum isnt it.

cheers 72-van
 
Hi mate you be ok i did the same i hadnt much experience before with three phase testing
college provides everything
i have multifunction megger 1552

so did the college for assesment 2 and 3 of the practical for the 4th assesment on the three phase and single phase i had to use a fluke 1553 i think it was had no experience with this meter only a quick showing of how it worked of the college tutor the only difference with the fluke is for live tests the fluke you have to use all three leads as the neutral blue lead is used to power the meter so has to be connected to neutral bar of the ccu when doing Ze and PFC (pefc green lead to earth bar blue lead to neutral bar and brown lead to line at incoming supply side of main isolator with all loads removed main switch isolator off and locked off labelled etc key always in pocket
pscc green lead to neutral bar and blue lead to neutral and the brown lead to line highest of the two recorded as pfc)
with the megger only two leads needed

when doing pfc on the three phase which is the origin and the one to be recoreded the highest pfc will between the lines
but as this test is not done so
measure all three lines to neutral seperatley ie
L1 to N = 0.546KA
L2 To N = 0. 560kA
L3 To N = 0.550kA
the highest of these should be multiplied by 2 this figure errs on the side of safety eg allows for not being able to test the L1-L2, L2- L3, L3-L1
the highest pfs will always be between the phases so
whichever of the lines to neutral is the highest eg
abve L2 - N = 0.560kA X 2 = 1.12kA
which is what is recorded on the PIR and the schedule of test results
hope that s a bit more help mate I did a post somewhere with all whats required for the practical somewhere and others have done loads of posts just keep reading everything on here
GN3
Bs7671 especially section 7
memorandum of guidance on elecy at work regs
gs38
all the other books etc been recommended to you
and you should be ok
best one for giving you a feel of exam is exam success
most important one to read GN3
for practical info cristopher kitchers guide to inspection and testing the best
practice
calcs, writing test procedures, efli diagrams all systems with fault path and fully labelled also practice drawing with a fault on the line to neutral as this comes up sometimes instead of efli
good luck matey
 

Reply to Any Non sparks done the 2391 course ?? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

S
The coding part is all down to experience and knowing whether something is right or wrong. Remember some pics have no faults.
Replies
2
Views
228
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
965

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top