Hi All

Just wondering how you guys approach requests for downlight installs. Upto now I only attempt them if have access to floor boards above or the ceiling has been temporarily dropped so have easy wiring access. If ceiling is the more modern suspended type ceiling obviously not a problem to wire them. But how do you access this to the point you feel comfortable going ahead with it. Concern is take on a job that appears to be suspended and has ease of wiring start chopping away for downlight holes and then find there's either wooden supports or some sort of hindrance for the wiring
 
You might be able to stack two of them for extra thickness.

But I guess if it is properly earthed then at least it will force disconnection even if someone keeps drilling/nailing against the resistance of the sheet.
Stacking 2 or more would not provide the same protection.
And the intention of this particular method of complying with 522.6.204 is that it need not be earthed.
 
which brings me back to my post... why not nominate in line with lights as safe zones similar to walls? the method would then comply.

cost being a factor, it's way less expensive than cutting and repairing huge holes, and eliminates the risk of drilling blind through joists, trying to miss any cables etc.that can't be seen.

apart from which, it's farless likely to be screwed or nailed than a cable in a wall.not many customers want to hang pictures or fit shelves on a ceiling.
My approach, for what its worth, is,

1, Find a joist, look for popped nails, sags, split joints. IDEALLY close to the existing rose, this will allow you to relocate/extend existing cables to first new light position.

2, cut in a 100-150mm hole on one side of the joist. To allow access for angle drill. Number the balnk and ceiling and draw a line across the cut to to aid with relocating.

3, use a fish rod to gauge distance between joists, use phone camera to have a scan round.

4, repeat alongside all joists that need drilling. This will give you all the visuals you need. Only now can you make a reasonable stab of planning the locations and and should avoid hitting any snags.

5, using these holes, often upto 4/5, you can see both sides of any joists that need drilling, so you can now drill your routing holes in the joists.

6, drill out the light holes, fish in cables, test and energise.

7, to fill the routing holes I use any suitable timber on site to make battens, fix two across the hole. Use the numbers and marks from earlier to fix the correct blank back in its hole.

8, Use easifill and a small filling knife to fill the deeper parts then a large (150-200mm) filling knife to skim over, let dry and sand. If the holes are still visible after sanding give them another skim. Should be invisible after painting.

If its lath and plaster make your excuses and leave..

If artex, new ceiling. Its awful stuff and should be illegal.
 
Stacking 2 or more would not provide the same protection.
And the intention of this particular method of complying with 522.6.204 is that it need not be earthed.

And if you earth it then how do you ensure a good connection, and one that is accessible for checking? Earthing the plates is not the way to go.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Approach for downlight install requests
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
53
Unsolved
--

Advert

Thread statistics

Created
JohnS888,
Last reply from
DPG,
Replies
53
Views
10,047

Advert

Back
Top