Octopus

So I got a call from a customer asking me about something I did in Feb 16 - so I duely paid a visit. Knowing they had had some work done I asked if I could see the certificate..... as I didn't take mine with me!

Now bearing in mind a new fuseboard had been fitted, the kitchen had been hacked around, downlights had been fitted and a wall removed I was expecting an detailed EIC........

Er no, the EIC simply said replacement fuseboard..... which had all 10 "slots" used.

This is a photo of the test results sheet.........

Test results.jpg


Sorry its side ways

Anybody want to play "spot the mistake / ommision / unusual entry" with me?
 
Ring final 9 appears to be rather long and open circuit on the lines. Seems they didn't loop it either or several of the others.
They also have 4.0 cpcs on the 6.0 cables, assuming T&E.
No IR readings.
 
Dear me, I could have fabricated a better test sheet sitting at home with a cuppa!
Not supposed to put LIM on an EIC.
There's and old saying "If it looks right, then it is right"
This clearly isn't right.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Are you based in Frimley????????
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36
Unsolved
--

Advert

Thread statistics

Created
Octopus,
Last reply from
sparkdog,
Replies
36
Views
3,242

Advert

Back
Top