Can anybody tell my why you can only remove an ATEX isolator front off when it's in the on position??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss ATEX Isolator front removal? in the UK Electrical Forum area at ElectriciansForums.net
I'd guess it is so the isolator cover cannot be removed when the isolator has been padlocked in the off position by someone (such as a fitter) doing maintenance.
Can anybody tell my why you can only remove an ATEX isolator front off when it's in the on position??
Installs in a zoned area can be done by any electrician, it's just the person whom commissions it that needs compex.Usually an isolator for 3phase within an Ex environment will be Ex.d. There is a lot of design time that goes into producing one of these. For a start it has to potentially contain an explosion.
ATEX work can only be undertaken by competent persons, manufacturers could make an isolator completely idiot proof, your just going to pay more than you already do!
Installs in a zoned area can be done by any electrician, it's just the person whom commissions it that needs compex.
Define competent? all i'm saying is that anyone can install hazardous area gear, you just need a compex person to check it.No it can't.
It can be done by anyone competent.
Define competent? all i'm saying is that anyone can install hazardous area gear, you just need a compex person to check it.
Define competent? all i'm saying is that anyone can install hazardous area gear, you just need a compex person to check it.