Sorry didn't read the regulation properly. This is acceptable and provided it is part of the multicore cable its acceptable.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bare CPC's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
mark28118:This is acceptable and provided it is part of the multicore cable its acceptable.
Where the sheath of a cable incorporating an uninsulated protective conductor of cross-sectional area up to and including 6mm^ is removed adjacent to joints and terminations , the protective conductor shall be protected by insulating sleeving complying with BS EN 60684 series.
I only ask because I'm currently working in afghanistan and we are basically going over alot of american work and faulting it to our regs, in their NEC code they allow bare CPC conductors but I got told to BS7671 anything over 6mm didn't need sleeveing. But guess they were wrong. Thanks for the quick reply's
Hi E54,
I posted the full reg, and it does not say cables above 6mm^ have to be sheathed, it only says cables up to and including 6mm^ do.
You could infer from that reg that above 6mm^ don't need to be, as that what it is suggesting.
Bloody regs, never give you a straight answer lol, I am not talking 'best practice' here btw so don't shoot me lol.
Reply to Bare CPC's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net