Some fixed current-using equipment including ventilation and luminaires is allowed in zone 1 but must be IPX4, IPX5 if exposed to water jets.
No restriction in zone 2 but must be suitable for the environment - see manufacturers' instructions.
This work will still be notifiable after the changes.