If an installation is supplied by a two wire system (E.G. a TT system) , what are the benefits of using an earth electrode instead of simply joining earth to neutral at the supply head to create a TNCS system?

Surely using the supplier's neutral is a more effective return path for fault current than relying on the earth electrode and the solid mass of earth?

All replies welcome,

Cheers,
Crosswire.
 
My understanding of it is that PME is protective MULTIPLE earthing i.e. earthed at many points along the route to the suppliers stepdown transformer for the area. If the neutral breaks on a TNC-S/PME system there is more of a chance that there will still be an earth path for fault currents back to the transformer (I have no idea what the Ze would be in this scenario).

I agree. Sounds like a better system than one earth electrode hammered in at the installation origin with a (maximum) resistance of 200 Ohms.
 
I agree that the requirement for TT systems to include a residual current device at origin is definitely is a good thing, but again this requirement could easily be extended to all earthing systems.

I'm assuming it is only compulsory in TT systems due to the high resistance earth fault loop path, unless I am missing something?
I think adequate equipotential bonding and RCDs provide reasonable protection from electric shocks as long as they are not between Line and Neutral.
Do you believe it is good practice to use the supplier's neutral as TNC-S if you don't know if it is PME?
 
I think all systems dont have advantages to say, but they are chosen due to they're circumstance. TN-C-S has got to be safest with the DNOs having they're own electrodes in all the substations(say something go wrong with the supply side). TT I'd imagine that its used because TN-C-S can't reach to "out of no where" locations and meet d/c times, or the "earth" is more conductive in those locations and so provides better protection.

I'm not trying to be a teacher or anything so correct me if Im wrong.

Keen Learner :)

Forgetting TN-S, for starters.
 
I think adequate equipotential bonding and RCDs provide reasonable protection from electric shocks as long as they are not between Line and Neutral.
Do you believe it is good practice to use the supplier's neutral as TNC-S if you don't know if it is PME?

Again, I would never do this in reality. But I would be fairly confident that the suppliers neutral returned to the supply transformer and formed an electrical circuit, based on the functioning of the installation in question.

For this reason I think that it would make a good return path for fault current to operate the OCPD within the required time.
 
Again, I would never do this in reality. But I would be fairly confident that the suppliers neutral returned to the supply transformer and formed an electrical circuit, based on the functioning of the installation in question.

For this reason I think that it would make a good return path for fault current to operate the OCPD within the required time.
Neutrals break on TT systems in storms etc. that is why the supplier has not made them TNC-S.
 
To be totally honest, i'm amazed that a working electrician is actually asking the question in the first place!! Unless of course we are yet again, dealing with another 17 day/electrical trainee...

Thankyou for expressing your amazement.

I did notice a total lack of an explanation of the relative benefits of different earthing systems, however.

If I ever post a thread entitled " Please express your amazement!" , I will be sure to PM you.

Cheers,
Crosswire.
 
Please explain in further detail, if you would be so kind :)

There is far less to go wrong, and if it does, it's easily rectified. Both TN-S and TN-C-S are prone to faliure whereas a well installed TT system will outlast any other means of earthing. TT systems benefit from having noise free earthing. TT systems are far more cost effective from a suppliers point of view. You also have the benefit of having a true earth reference, rather than zero potential introduced by the star point, this is one of the reasons why TN-C-S is not allowed on final connection to caravans and mobile and transportable units.
 
Last edited:
There is far less to go wrong, and if it does, it's easily rectified. Both TN-S and PME are prone to faliure whereas a well installed TT system will outlast any other means of earthing. TT systems benefit from having noise free earthing. TT systems are far more cost effective from a suppliers point of view. You also have the benefit of having a true earth reference, rather than zero potential introduced by the star point, this is one of the reasons why PME is not allowed on final connection to caravans and mobile and transportable units.


Thanks dude
 

Reply to Benefits of a TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
668
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top