If an installation is supplied by a two wire system (E.G. a TT system) , what are the benefits of using an earth electrode instead of simply joining earth to neutral at the supply head to create a TNCS system?

Surely using the supplier's neutral is a more effective return path for fault current than relying on the earth electrode and the solid mass of earth?

All replies welcome,

Cheers,
Crosswire.
 
There is far less to go wrong, and if it does, it's easily rectified. Both TN-S and TN-C-S are prone to faliure whereas a well installed TT system will outlast any other means of earthing. TT systems benefit from having noise free earthing. TT systems are far more cost effective from a suppliers point of view. You also have the benefit of having a true earth reference, rather than zero potential introduced by the star point, this is one of the reasons why TN-C-S is not allowed on final connection to caravans and mobile and transportable units.

Define a well installed TT system.

While ever the IET perpetuates the myth of 200Ω being acceptable, TT will remain a 2[SUP]nd[/SUP] rate system.
≤1Ω is possible with a decent interconnected earth nest but you’re going to have to work for it. TT then becomes a viable if not a preferred supply system.

Having installed >20MVA of TN-S systems without problems due to fault. I’ll say it is the best system.

CNE (PME) in its purest form is good. something you’ll not find in this country.

As for the OPs question about a homemade PME, it’s shear folly.
 
Define a well installed TT system.

While ever the IET perpetuates the myth of 200Ω being acceptable, TT will remain a 2[SUP]nd[/SUP] rate system.
≤1Ω is possible with a decent interconnected earth nest but you’re going to have to work for it. TT then becomes a viable if not a preferred supply system.

Yes I suppose 'well installed' wasn't the right term to use, but what I was alluding to was a TT system with a sub 1Ω Ze. You can have well installed TT systems that aren't sub 1Ω, but as you say, I wouldn't then consider them superior, just different.
 
"As for the OPs question about a homemade PME, it’s shear folly."

I have never done this. The reason I started the thread was due to a colleague of mine conducting a Ze test on an old TNS system, and finding the external earth path not meeting the required values. (0.8 Ohms I believe)

He resolved this by driving an earth rod to convert the system to a TT, thus allowing a Ze of 200 Ohms.

He later spoke to a friend of his who works for a DNO, who ACTUALLY TOLD HIM that he would have been better off converting the TNS system to a TNCS system HIMSELF, and using the suppliers neutral as the earth fault loop path!

This is the background to my initial post.
 
well then, that DNO employee is a dork. how would you know if the supply was PME before you did that?


I guess I wouldn't know. It just got me wondering about the reasons for selecting different types of earthing systems and what the advantages or disadvantages would be of each type might be.

I was hoping a spark with a more in depth understanding than myself would shed a bit of light on the subject so I can improve my own knowledge, and I'm pleased that a couple of forum members have been very informative and helpful. :)
 
lol .
 

Attachments

  • [ElectriciansForums.net] Benefits of a TT system?
    digging-a-hole.jpg
    230.3 KB · Views: 107
*sigh*

Thanks to all the helpful members.

To all the trolls, please continue amusing yourselves by mocking me for asking a technical question.

I notice, btw, that none of the trolls have actually put forward even the slightest analysis of the different types of systems. Interesting........
 
*sigh*

Thanks to all the helpful members.

To all the trolls, please continue amusing yourselves by mocking me for asking a technical question.

I notice, btw, that none of the trolls have actually put forward even the slightest analysis of the different types of systems. Interesting........

I think enough has been said, to tell you the truth:confused:
 
It seems that risk of broken neutral is one of the primary concerns.

Why is it high for TNCS systems , and low for TT systems?

An earlier poster said that due to TT systems being used for remote locations, there was a high chance of losing the neutral via a storm (and therefore also the fault return path if the neutral was used as such). This is the reason for driving an earth electrode in a TT system, which seemed to make sense.

What am I missing?
 
In a TNCS the fault path uses the neutral (yes I know you know that) so if the neutral breaks and there's a fault inside the installation then you could have every metal part inside it live. In a TT you still have the fault path through the general mass of earth.
TTs are not just used in rural/remote locations, we live near a main road into a fairly busy town and we're on a TT (Ra > 1 ohm)
 

Reply to Benefits of a TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
668
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top