As we all know the first thing to do when conducting a periodic inspection, is to inspect.
So finding a missing blank or a damaged socket should not involve de-energising any circuits.
So the question is, are you going to de-energise the affected circuit knowing full well that you will not re-energise the circuit before the C1 condition is rectified?
To my mind a code C1 is where there is a danger of injury to persons or livestock or of a fire without there needing to be another fault.
A code C2 is as above, but where it would require another fault before injury or a fire could occur.
An exposed live conductor or conductive part would be a code C1.
A broken CPC or lack of earthing, would be a code C2.
The problem I see is that unscrupulous electricians could use this to code C1 for things that are not actually C1, thinking they will get extra money to rectify said fault.
Would you re-energise a circuit that has a fault in which all conductive parts on that corcuit are live?
Reply to Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
There is no homework, and I'll never see these photo again.
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...