I would 99.9% of the time code a missing blank as C1 and I rarely give C1's.

It's a great big hole with a big piece of live copper behind it which is easily touchable!

What circumstances would the 0.01% occur?

As mentioned earlier I would NOT C1 it as I would pop some spare blanks on to bring it up to standard. I always carry them and it costs minimal pennies and vertically no time.

However for those lazy penny pitchers who wouldn't do this I think a C1 should apply.
 
Isn't C1 classed as "immediately dangerous" rather than danger present.
Self explanatory definition in my opinion.

If an exposed live part does not have suitable basic protection to prevent it being touched. That to me is immediately dangerous.
No it initially states Danger Present. Later it explains there is risk of injury. Immediate remedial action required. Strangely it also explains Code 2 as urgent remedial action required. What is the difference?
This is the issue I have with how they are defined. What is Danger Present which overrides Potentially Dangerous.
 
Merlin Gerin and Schneider boards have sliders to energise each way.
If those sliders are off where there are no MCBs, where’s the exposed live conductive parts?
Similarly old MEM DBs have removable ‘Y’ shaped pieces of metal to connect between the MCBs and the hidden bus bars.
Most CUs have shrouds and bus bars which can be cut to length.
So like I said code C2 for missing blanks and code C1 where there is exposed live conductive parts.
 
This is my point on the Code definitions. Separate Danger Present and Potentially Dangerous, they walk the same path to a hazard. What is Danger Present, something Potentially Dangerous.

I am not sure if you are being deliberatly obtuse but I will play the game with you.

If you read it literally then everything has the potential to be dangerous. If we use common sense it is very obvious what the intention is.
 

Reply to Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
620
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
308

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top