Blowing sockets and popping RCD | on ElectriciansForums

Discuss Blowing sockets and popping RCD in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 27, 2022
Messages
42
Reaction score
11
Location
London
A client asked me to add two sockets in their bedroom

I took power from two sockets in the lounge which is behind the bedroom wall.

I ran a cable out of each socket for the new socket

The problem is it now is tripping the RCD and blowing the old Existing sockets and light switches

But the new sockets I added still work fine

The old existing sockets and switche are blown and unusable

When I try to reset the RCD It pops and Sparks down

Any idea to why this is happending
 
if the old sockets were on a ring, and one leg has popped out... the new sockets, being connected will still work, but theres maybe another floating live touching the metal back box.

can you take photos of the back of the sockets? there might be something obvious to us that you havent seen
 
if the old sockets were on a ring, and one leg has popped out... the new sockets, being connected will still work, but theres maybe another floating live touching the metal back box.

can you take photos of the back of the sockets? there might be something obvious to us that you havent seen
The thing is the client phone back saying there’s no power and the RCD is popping down and sparking so I went back same night, and opened up the sockets I touched the connections were fine the socket sparked and popped while the socket was open so no loose lives
 

Attachments

  • [ElectriciansForums.net] Blowing sockets and popping RCD
    54001265-E860-4A32-9457-62D59B700C4E.jpeg
    370 KB · Views: 67
No tests on the ring were carried out
So how do you expect to find the problem without testing? Apologies if I’ve got the wrong end of the stick here, but if I’m dealing with a symptom of tripping pretty much the very first thing I do is IR testing
 
no the actual sockets sparked and blew in front of me
The mcb never tripped once only the RCD

On the assumption you're trained and experienced, what does that tell you ?

so I went back same night, and opened up the sockets I touched, the connections were fine, the socket sparked and popped while the socket was open so no loose lives

Did you leave the socket sparking and popping when you left or have you isolated it / them?
 

Reply to Blowing sockets and popping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
585
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
623
davesparks
D

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top