Best Practise Guide No2 - Consumer Unit replacement in domestic and similar premises says the following on Page 5 (note 3)

"A 6mm main protective bonding conductor size could be deemed adequate where the minimum size required by regulation 544.1.1 of BS7671 is 10mm if the bonding conductors have been in place for a significant time and show no signs of thermal damage."

So it looks like you're ok as long as you meet those 2 criteria.

Also worth looking at note 2 on the same page (5) which mentions certain criteria for using a 6mm main earthing conductor.

http://www.esc.org.uk/fileadmin/user_upload/documents/industry/best_practice/BPG6_09.pdf

I had totally overlooked using BPG 2 which clearly points out what is permissible on a board change.
I was correct with regards to checking the bonding for thermal damage and corrosion if less than 10mm for continued use. I had also confirmed the adequacy of the earthing conductor by applying the adiabatic. On existing installations where a board change is needed i will from now on make reference in the 'extent of works' box that the change has been completed in accordance with BPG 2.and will note any departures found in the relevant box on the EIC.
 
As far as the bonding cables go, both water and the gas bonding cables should be connected between the service pipes as they enter each flat, and the flats MET (which is an installation EMT) not to the buildings intake position (MET).


As this is a TNC-S (PME) installation, a minimum 10mm main earthing conductor should be run in with the 16mm T&E. I'd personally, never even think about running/using T&E as a sub-main cable to supply flats, even for TN-S systems, it just smacks of amateurism to me!! ...lol!!

I appreciate your view on this mate. If this was a new installation i also wouldn't consider using a t&e cable for the main supply and would use the sizing tables for the required earthing over the use of the adiabatic, however, this is an existing installation with very limited to no possibility for upgrade.
As a thought, as the flats have separate supplies fed from individual switch fuses at the intake and the service belonging to each flat are bonded to these wouldn't this be classed as satisfactory as the M.E.T within the switch fuse could be classed as part of that installation only?
 

Reply to Bonding issue upon upgrading fusebox. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
108
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
905
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top