davie spark
If the' part' is part of the electrical installation or it is bonded to part of the electrical installation, you do an earth continuity test.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss bonding services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
To test if something is extraneous do you not do an ir test to earth
To test if something is extraneous do you not do an ir test to earth
Only if the part is not already bonded, if it is already bonded, as it might be, you would carry out and earth continuity test on the bonding conductor. Whilst not wishing to confuse this thread further, there are instances where extraneous conductive parts may be required to be bonded (to provide equalisation of voltage under fault conditions), but not earthed and where transformers and data wiring is present the testing of non earthed bonding of these types of extraneous parts can only be confirmed by earth continuity testing.
0.05 ohms, dont think its a reg but is in some guidance and learning books
ALSO THE ADIBIATIC IS NOT FOR MAIN BONDING AS THESE ARE SPECIFIED, BUT CAN USE TO CHECK OLDER INSTALLATIONS??? IL READ YOUR AWNSER WHEN I SIGN Back on, gotta shoot, cheers wise one, i will learn regs inside out and make you proud... and earn myself a small fortune is the plan...
GN3 2.7.5 Continuity of protective conductors including main and supplementary bonding. Test Method 2. The “water is muddied” here in the usual IET fashion, by a less that explicit inference, that leads to alternative interpretation.The 0.05 Ohm figure is between parts that require supplementary bonding but NOT back to the MET.
There is no maximum resistance specified in BS7671:2008 for main protective bonding conductors.
Short answer, you can combine both bonds in one cable as long as you don't cut the cable. Double over the cable at the first bonding point and fit a crimp of suitable size, then bond the remaining utility using a crimp suitable for the cable size. Appropriately label the conductor at the main earth terminal.
GN3 2.7.5 Continuity of protective conductors including main and supplementary bonding. Test Method 2. The “water is muddied” here in the usual IET fashion, by a less that explicit inference, that leads to alternative interpretation.
“To confirm the continuity of a bonding conductor, the leads from the instrument are connected to each end of the conductor and a reading is taken. One end of the bonding conductor and any intermediate connections with services may need to be disconnected to avoid parallel paths.”
“This method can also be used to confirm a bonding connection between extraneous-conductive-parts where it is not possible to see a bonding connection, e.g. where bonding clamps have been 'built in'. The test would be done by connecting the leads of the instrument between any two points such as metallic pipes between which a bonding connection was required and looking for a low (minimal deflection) reading of the order of 0.05 Ohms or less.”
IMO this does apply to Main Bonding Conductors by inference.
The resistance (R) of Supplementary Bonding Conductors between simultaneous accessible exposed-conductive parts and extraneous-conductive-parts need only meet the generally less onerous (most domestic installations certainly) R<= 50V/Ia in an AC system where Ia is the operating current of the protective device, for RCDs Idelta n and for overcurrent devices, the current cause automating disconnection in 5s, 415.2.2