when you main bond services, does this not take away the need for supplementry bonding.......???? is what i believe but hesitant now....
As I understand it, supplementary bonding is used to limit the potential difference between exposed or extraneous-conductive-parts to ≤ 50V.
The impedance between any exposed or extraneous-conductive-parts should be low enough to meet the above requirement.
Let's say you have a 7kW shower on a 32A Type B breaker. The current required to operate the breaker is 160A so the impedance between the exposed-conductive-part of the shower and any other exposed or extraneous-conductive-parts of the location should not be more than 50V ÷ 160A = 0.31Ω.
This may not be achievable through main protective bonding alone so supplementary bonding is used. Of course RCDs do away with the need for supplementary bonding in most cases as the maximum impedance increases to 50V ÷ 0.03A = 1667Ω