Ah, I see where our points meet a hurdle now. As far as I can tell we agree on everything but this, which in itself is more of a mute point than anything else.
Quite fundamental, really. You said the opposite of what I wrote.
As you rightly said, you would be measuring first each and every exposed and extraneous conductive part back to the MET to ascertain its effectiveness. If it is higher than 0.05 then it can be argued that its connection to earth is not effective,
No, no, no.
The 0.05 has NOTHING to do with it.
If you think that then no lighting circuit (1.0/1.0) is ever going to comply.
Even a shower with 4mm cpc would have to be less than 11m.
0.05 is only used as a test for a good connection.
by this alone you would have worked out that this part will need supplementary bonding.
No. The impedance of two correctly connected parts could easily add up to more than the required figure of 50/Ia so supplementary bonding will be required.
Let's say for example that you have five extraneous conductive parts within a bathroom and all but one are effectively connected to earth, then the solution would be to supplementary bond that one part to another that IS effectively connected to earth.
No. Connect the ineffectively connected part.
They, then may still require supplementary bonding.
Simply adding an RCD would not be sufficient without first supp bonding it as required.
Yes, it would as long as the other two conditions are met.
That is - disconnection times comply. This will mean the cpcs are effectively connected and
Main bonding in place. Depending on the size of the property, the impedance from pipe to MET could be relatively high - doesn't matter.
The very reason for supp bonding in this instance has got nothing to do with the 50/Ia equation, it is purely to do with having each part effectively connected to earth.
No, it is the other way round. 50/IA is the criterion for
supplementary bonding
because the resistance
between parts is relatively high because of the path from pipe through main bond to MET through cpc to appliance.
This CANNOT posibly ever be less than 0.05 (unless teeny-weeny flat).
A personal experience was an EICR I did on a bathroom where the basin on one side of the room was run in polyplumb under the floor.
It was therefore NOT extraneous.
Each and every part back to the MET was under 0.05ohms
Teeny-weeny flat or already bonded.
except for the basin tap which was around 6kohms.
How can a plastic pipe have a reading of 6kΩ ?
Taps are never extraneous. You should test the pipe.
Measuring between each part conformed with the 50/Ia equation apart from the basin tap.
That's possible but the 6kΩ is a mystery.
The house was RCD protected. Solution: Supp bond the basin tap to the radiator on the adjacent wall. Sorted.
Sorted yes but if the other two conditions were met (ADS and main bond) then not necessary.
I stand by what I wrote in post #21.