Thanks for a great educating post, I have learned a thing or two.
Can I confirm I have got my head around this subject correctly.
To test if something is extraneous, IR test @ 500V between main earth and the part in question, if below 45k ohms then considered extraneous (why 45k ohms)?
Then continuity check between part and MET value must be below 50v / Ia or the part in question will require supp bonding regardless of RCD protected or not as it is considered to not be effectively connected to earth?
Also, you should continuity test between all extraneous and exposed conductive parts in a bathroom and the resistances between these parts should again be below 50V / Ia? Again if not then sup bonding is required regardless of RCD Protection?
The lack of sup bonding if calculated and measured to be required is therefore always a code 2 regardless of rcd protection?
Thanks
Craig