I have recently done an EICR test on a flat. The only issue being that the water pipe is not bonded at the stop cock. The stop cock itself is located just outside the flat front door in a service cupboard - the trouble is the pipes are all plastic in the service cupboard and under the floor into the flat.
It seems to be that all pipe on show is plastic, the only copper pipe I have found is in the water tank cupboard which is nowhere near the point of entry or the stop cock and is permanently screwed shut.

My question is where should I bond it?
 
If you are not going to test it to prove it isn't extraneous, you will have to bond it.

If you can prove it isn't, then don't.

Parallel paths to earth via cpc's on boilers and such like will obviously make below the required 22k ohms. But if you cannot or will not disconnect them and PROVE it isn't extraneous then bond it.

That's the way I see it anyway...
 
I have recently done an EICR test on a flat. The only issue being that the water pipe is not bonded at the stop cock. The stop cock itself is located just outside the flat front door in a service cupboard - the trouble is the pipes are all plastic in the service cupboard and under the floor into the flat.
It seems to be that all pipe on show is plastic, the only copper pipe I have found is in the water tank cupboard which is nowhere near the point of entry or the stop cock and is permanently screwed shut.

My question is where should I bond it?

HERE IS THE TEST!!! QR code 2 -- Protective supplementary bonding test - YouTube
 

Reply to bonding to water pipe. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I understand your question and it can be a can of worms, on the one hand as mentioned in your previous reply is it a extraneous conductive part...
Replies
2
Views
589
  • Question
edit : It was Emma Shaw that got electrocuted, Lisa Shaw was killed off by the rona jab.
Replies
4
Views
2K
K
  • Article
Seeping pipe connection to Loft Cold water Had a problem with hammering noise coming from pipes (triggered by hot water, though it could be eased...
Replies
0
Views
128
KennyA
K
  • Question
Ok. Thanks
Replies
6
Views
1K
M
  • Article
Cold Water Tank In Loft - Cause Of Flood Dispute? Having just moved into a property and discovering the central heating not functioning, after 3...
Replies
0
Views
196
Mijacmad
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks