ok so the installation is left in its normal state energised, the bit that confuses me is 2 readings are taken and the highest recorded, what terminals are the two readings taken from.
Phase to Neutral followed by phase to earth and the larger of the two readings recorded,
P-N = PFC Readings taken between Phase - Neutral on incoming terminals of main switch
P-E= PEFC Readings taken between Phase terminal of main switch and earth bar in the cu.
On a TNS and TT you will get two different values of which the highest should be recorded.
On a TNCS both readings should normally be the same or thereabouts.