Currently reading:
British General outside socket

Discuss British General outside socket in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Hi People on an install I have come across a British General outside socket that is reducing the Insulation Resistance when i remove the outside socket the IR goes back up has any one come across this before
Thanks phil
 
As above, if it's an RCD socket then it will give a low reading. A 500v test may cause damage to such a socket. Otherwise if its a standard socket you can always IR the terminals of the disconnected socket to verify.
 
What, are the IR readings with, or, without the socket being connected? Does the IR alter if you just slacken the front plate from the back box?
 
Last edited:
neon should only affect the IR if the socket switch is in the ON position.
Agree Tel but we have nil info on test results or how the tests were carried out.
[automerge]1587745759[/automerge]
Hi its between line and neutral the line conductors and cpc are fine I am not on site but I can not recall it having a neon but could be a poss
phil
As per Tel' response, test with the socket switched off, or removed from yje back box bye still connected, AND GIVE US THE RESULTS OF YOUR TESTS PLEASE.
 
If it is one of these then it is the neon most likely:
https://www.NoLinkingToThis/p/briti...dp-weatherproof-outdoor-switched-socket/67928
[automerge]1587748954[/automerge]
Out of curiosity has anyone used one of them? For £10 it seems very cheap but maybe it is OK.
 
If it is one of these then it is the neon most likely:
https://www.NoLinkingToThis/p/briti...dp-weatherproof-outdoor-switched-socket/67928
[automerge]1587748954[/automerge]
Out of curiosity has anyone used one of them? For £10 it seems very cheap but maybe it is OK.
or both of them. but only in circuit with switches ON. and i think BG are using LEDs instead of neons, these days.
 
I use BG IP sockets, they are fine....and fitted with neon indicators. If the OP is testing L-N then that would be the reason for the low reading.
To the OP I would suggest you should only carry out a L-N test on a new known circuit where you can be certain all loads are out of circuit. A 500v test L-N can damage some equipment and if you continue to test L-N without checking it is inevitable that eventually you'll damage something expensive. On existing circuits where you cannot be absolutely certain what is connected a LN-E test is perfectly acceptable and is much safer. If you must carry out a L-N test always start with a soft test at 250v.
 

Reply to British General outside socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock