hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
u aint just a pretty dude tony are you.... when i was working there today i found half pack of 5A fuses lying on top of cu .
would you say with the fuse keep blowing would destroy the lamps aswell in some way.
 
also, it's common for the fuse to blow when a lamp fails (more so with MCBs). an anti-surge (motor rated) fuse may cure your problem though.
 
well that sounds great telectrix would they fit in to the 1361fuse carrier or am i going to have to change..., i was thinking of changiung the fuse carrier to a 15A one
 
bad idea.15A is a tad to high a rating for 1.5mm T/E . even worse if it's wired in 1.0mm. better would be to split the lighting into 2 5A circuits.
 
isnt 1.5mm rated at 18-20A or something tel. too much work involved in splitting the lighting circuit. ive told them to change to energy efficent lighting (led) just weighing up mu options for monday morning
 
10A fuse in the FCU, would be better. even better would be to replace the GU10 halogens with LEDs. ssimmples
 
But remember a fuse is there to protect the circuit from damage so you still have the problem of an oversuze fuse at the origin of the circuit.......theres nothing to stop someone removing the fcu in future and just relying on the fuse at the board which at 15A is too much for 1mm............
 
1mm can take 16A if i remember right, the circuit is 1.5mm t&e. i aint as expierienced as i think i am so keep them comming sparkys.. where you get a 10A fuse tel, never seen one before or have i, naw i i havent hey
 
good point. glenn. methinks I=P/U is looking for a quick fix. not a good idea. could try a 6A or a 10A MCB though , after a 15A fuse in the board.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
-
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
bs 1361 fuse
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
76
Unsolved
--

Advert

Thread statistics

Created
i=p/u,
Last reply from
i=p/u,
Replies
76
Views
11,804

Advert

Back
Top