i=p/u

-
Arms
hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
That is because the new amendment as deleted the reference to the BS 1361 fuse i-p/u and now refer to the BS 88 series

I remember you lost your BRB book if you have the OSG it will be on page 102 table i for 0.4 secs

they are

Zs 5amp 8.4 ohms

Zs 15amps 2.6 ohms

Zs 20amps 1.4 ohms

Zs 30amps 0.81/0.93 depending on you CPC size
 
lenny if you out there, have you ever seen of a fuse that acts like a type c mcb its for a 1361 5A circuit thats tripping with the inrush of the halogens??? just asking as i seen you have a fuse shop .
 
well was just about to say that glensarks, when i was looking the other day at sockets when tripped all fuses were bs88 for sockets which were all in one board and then all the lighting is in one board. now all lighting circuits are 5A do i need to change the fuse carrier to 15A and are these easy to get. or could i just get bs88 hbc 5A fuse
 
Dont forget, BS88s are very common in industrial applications and most (not all) but most industrial loads are inductives so my thinking is you will probably be able to get a BS88 thats suitable......
 
aye i want the easiest option as my practical skills on boards are dunce.lol i know having a fair idea is broc.

i can see delay hbc fuses but these are only protected upto 1.5kA,
 
anyone else got any more input as i have to go to this job in morning. just a reminder bs1361 fuse blowing when 18 halogen lamps are turned on. how would you tackle it???

too now i am going to cef in morning to see if i can get 5A hbc fuse and hope delays the start up current needed from blowing fuse and see if that sorts it.
 
Last edited:
just wondering would a 5A bs1361 fuse have different charcteristics to 5A bs1362 fuse???? could this be anything? thanks for your input on this post guys

think they are replacing blowing fuses with the plug type 1362 instead of 1361
 
Last edited:

Reply to the thread, titled "bs 1361 fuse" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top