i=p/u

-
Arms
hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
HALERS lol BTW any scottish lads I hear the rep is "eyecandy" Might need to give her a wee call
Did a rewire on this kitchen a few weeks ago....lovely bird she was....we had to go back to put a new central heating timer on for her earlier today....slurp...lol..
 
well i think change the lamps is easies option, what about that fuse that allows inrush currents tel, do they exsist that will fit in 1361 fuse carrier. if i changed to 6A or 10A mcb wouldn't that mean the zs would change and maybe not meet the requirements.
 
i=p/u The steady current drawn by a lamp is when it is at its operating temperature which for incandescent lamps is around 2000 deg C the initial current draw at 25deg C can as as much as 5 -10 times the steady current. So switching all switches together gives a massive surge just like a motor starting current.
Put in the largest fuse permissible for the circuit cable and advise customer to switch the switches one at a time
If you uprate the fuse you need to confirm the Zs still meets the 0.4 disconnection time
 
Last edited by a moderator:
so you with me platty in chancging the 5A fuse carrier to 15A as it is on 1.5mm t&e, its a dr's surgery so they can take instructions and only the sockets are rcd protected
 
Can you replace the cable with a 2.5 at the board then into an enclosure with a C type breaker in and then using the installed cable....out to the lamps?........
 
was thinking c type breaker too but why 2.5mm for 15A fuse. am i missing something reallly badly here.. do you think would still trip the blow 15A fuse, the type c breaker does sound the pigs ears
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
 
Last edited by a moderator:
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
yep. got it platty (p) 282...thank you. :crazy:
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A

Think a GU10 Lamp holder might not come under that regulation
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
-
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
bs 1361 fuse
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
76
Unsolved
--

Advert

Thread statistics

Created
i=p/u,
Last reply from
i=p/u,
Replies
76
Views
11,805

Advert

Back
Top