hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
well i think change the lamps is easies option, what about that fuse that allows inrush currents tel, do they exsist that will fit in 1361 fuse carrier. if i changed to 6A or 10A mcb wouldn't that mean the zs would change and maybe not meet the requirements.
 
i=p/u The steady current drawn by a lamp is when it is at its operating temperature which for incandescent lamps is around 2000 deg C the initial current draw at 25deg C can as as much as 5 -10 times the steady current. So switching all switches together gives a massive surge just like a motor starting current.
Put in the largest fuse permissible for the circuit cable and advise customer to switch the switches one at a time
If you uprate the fuse you need to confirm the Zs still meets the 0.4 disconnection time
 
Last edited by a moderator:
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
 
Last edited by a moderator:
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
yep. got it platty (p) 282...thank you. :crazy:
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A

Think a GU10 Lamp holder might not come under that regulation
 

Reply to bs 1361 fuse in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
152
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
962
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top