Hi folks

Trying to make sense of the Regs regarding RCD types for a standard 13A socket intended for electric vehicle charging. Looking at 722.531.2.101 in the 17th edition Amd. 3, type A seems to suffice unless DC residual current is known to exceed 6mA, in which case it is type B. So how do I know if the DC residual current exceeds 6mA? Do I get this info from the charger manufacturer? What if the user changes car/charger?

Under 18th regs type B is required unless the equipment (presumably the charger) provides protection against DC residual currents exceeding 6mA.

So, do I fit a type A or B, or does this depend on the specific charger? If B, can anyone point to one - when searching for type B RCBO I just get ones with type B curve overcurrent protection. And according to the 17th it ahould be 'at least an RCCB or RCBO'. Does this preclude an RCD fused connection unit?

Finally I've read on other threads about notifying the DNO about new EV charging points - does this include 13A sockets intended for EV charging?
 
Code of Practice for Electric Vehicle Charging Equipment Installation - The IET - https://www.------.org/resources/standards/ev-charging-cop.cfm
Thanks! Am aware of it, but can't justify the cost (yet). One day, for sure, but there may be a new edition by then...
 
Noting I'm no expert, my read is B for a socket and then you've covered 18th and not being able to confirm 6mA DC protection is going to be provided.
 

Reply to BS 1363 socket for EV charger - what kind of RCD? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top