HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,279
Reaction score
6,527
Location
Gloucestershire
This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?
 
Last edited:
One thing I would say is that if you are going to extend a circuit protected by a BS 3036 fuse then the correction factor of .725 would have to be applied to this circuit . the only thing I would do is to use a fused spur to feed an additional point or RCD fused spur if required ...
 
Yep me too. If thats whats required.

HHD next time you meet that assessor, ask him how he feels about 13A fuses, and the like, as they are effectively just like a rewireable, as in, a bit of "fuse wire". Ask him if he thinks every house in the country needs a circuit breaker fitting at the service head instead of that silly great fuse wire thing.
 
You can use any protective device so long as you meet the disconnection times. BS3036 fuses are still listed in BS7671 so as long as the measurements and calculations work out, they are fine.
until some complete moron of a customer fits a nail in.
 
Late to the debate, but totally agree with the consensus, the assessor is wrong. As has been stated, if the circuit Zs falls below the adjusted max Zs value (0.87 for 30 amp, iirc), your good to go.
Oh, and ask him which Reg he is using to justify his comments.
 
In the new 3rd edition/cash cow if you added a circuit to this CU would have to add a RCD or do it surface glav or in glav in the fabric of the building or more than 50mm deep in the building. And this is the best in a building with an electrically skilled person you have to do a risk assessment to say, why you deem it safe not to have a RCD.
 
[][/B]
In the new 3rd edition/cash cow if you added a circuit to this CU would have to add a RCD or do it surface glav or in glav in the fabric of the building or more than 50mm deep in the building. And this is the best in a building with an electrically skilled person you have to do a risk assessment to say, why you deem it safe not to have a RCD.[/QUOTE]
2nd bit in bold that's just for a socket outlet without RCD protection and if the installation requires RCD protection then you would have to put it on a RCD anyway.

And the 1st bit in bold you should already be doing this anyway but doesn't have to be galv when surface.
 
Last edited:
This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?

Jesus glad I'm not one of your client using a Regs book which as been out of date for 3 years
 
One thing I would say is that if you are going to extend a circuit protected by a BS 3036 fuse then the correction factor of .725 would have to be applied to this circuit . the only thing I would do is to use a fused spur to feed an additional point or RCD fused spur if required ...

Late to the debate, but totally agree with the consensus, the assessor is wrong. As has been stated, if the circuit Zs falls below the adjusted max Zs value (0.87 for 30 amp, iirc), your good to go.
Oh, and ask him which Reg he is using to justify his comments.

Not sure what you mean by 'adjusted max Zs' Polo? Page 55 BGB has the max Zs for a 30A BS3036 as 1.09?

Are you referring to appendix 14 BGB?
 
Jesus glad I'm not one of your client using a Regs book which as been out of date for 3 years


I dont think you quite understood the sentence. I have BGB.thought the 3036's would only be in BRB
 
Last edited:

Reply to BS 3036 fuses not allowed for new circuits!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
254
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
729
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
706

Similar threads

Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
570
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • Can you get a refund through Expedia?
    ๐”ผ๐•ฉ๐•ก๐•–๐••๐•š๐•’ ๐• ๐•—๐•—๐•–๐•ฃ๐•ค ๐•’ ๐•˜๐•–๐•Ÿ๐•–๐•ฃ๐•’๐• ๐Ÿค๐Ÿฆ-๐•™๐• ๐•ฆ๐•ฃ ๐•”๐•’๐•Ÿ๐•”๐•–๐•๐•๐•’๐•ฅ๐•š๐• ๐•Ÿ ๐•ก๐• ๐•๐•š๐•”๐•ช. ๐•‹๐•™๐•š๐•ค ๐•ž๐•–๐•’๐•Ÿ๐•ค ๐•ช๐• ๐•ฆ ๐•”๐•’๐•Ÿ ๐•”๐•’๐•Ÿ๐•”๐•–๐• ๐•ž๐• ๐•ค๐•ฅ...
  • {๐•๐•–๐•ฅ๐•“๐•๐•ฆ๐•–} Do you have 24 hours to cancel with JetBlue?+44-(804)-853-9001
    Do you have 24 hours to cancel with JetBlue? ๐•๐•–๐•ค,๐•๐•–๐•ฅ๐•“๐•๐•ฆ๐•– ๐• ๐•—๐•—๐•–๐•ฃ๐•ค ๐•’ ๐•˜๐•–๐•Ÿ๐•–๐•ฃ๐•’๐• ๐Ÿ๐Ÿ’ ๐ก๐จ๐ฎ๐ซ๐ฌ ๐œ๐š๐ง๐œ๐ž๐ฅ๐ฅ๐š๐ญ๐ข๐จ๐ง...
  • Low frequency humming noise in the apartment?
    Have you asked the neighbours? They might think it is coming from you.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top