Hi all,
My first post here, thought I'd see if it was possible to get some advice or tips...
Basically, I had a large amount of block paving and large concrete base laid at the far end (25m) of my garden a few months ago. Under this I had 3 core 16mm SWA laid.
(I most definitely can't vouch for the quality of the work done by any of these guys)
More recently me and my brother built a large garage on the concrete base and had an electrician add a new CU in the garage and connect the other end of the SWA to an MCB in the CU in the house.
Today, after about 2 weeks of not having any problems, the RCD in the house tripped out and wouldn't switch back on unless I turned off the MCB to the garage. It's worth noting, it rained fairly heavily last night.
After trying a few different things, I've eventually disconnected the SWA from the CUs at both ends.
I've tested for continuity across all cable/ armour combinations and noticed there's continuity (beeping) when I touch the live and armour.
Is my assumption that someone has damaged the cable, breaking the live wire insulation and water has entered this and created a circuit between the live and the armour a reasonable one? Are there any other ways this continuity could occur given both ends are now fully disconnected?
Assuming this assumption is correct, I'm curious if there's a simple way for me to locate this fault without digging up 30m of block paving?
For example, I was wondering if, by using a multimeter and testing the resistance across the live and armour at both ends I might be able to work out how far down the wire the break is?
So maybe if I got a resistance 10 times higher at one end than the other I can assume the damage to the 25m long cable is 10% (2.5m) from the end of the cable with lower reading?
I guess I don't need to be super accurate and that there are industrial tools that could accurately locate the fault, all I really want to know is roughly were to start digging in the hope of keeping the damage to the paving to a minimum.
Thanks in advance for any help or suggestions.
Dan
That leaves half of a pair of simultaneous equations and I gave up and opened the 1664 at that point. I’ll return to this one day…
To answer my own question in case anyone searches the forum for varley loop test in future…
The 2nd equation is derived from twice the resistance of a length of one conductor being equal R+X+y. Substituting that in leaves a ratio of resistance X to resistance of the total loop. I think.
I might try this and @pc1966 method out when I have time just for fun.
danielz000 - I am no more than 20 minutes drive from you. Do you want me to call in? If the method my colleagues have explained does not work on the damaged 25m length I will improvise a time domain reflectometer and use it during a second visit.
If he was my brother he would have been given an Essex smack for not waiting for some testing to be done ;-)
We will pass circa 50 Amps through the cable in order to produce a volt drop of the order 50 x rho = 50 x 0.00183 Ohm/A/m = 50 x 0.002 = 0.1 V per m or 25 x 0.1 = 2.5V over the length of the 25m cable. May even use an even larger current briefly.
Shall I buy the necessary items or do you want me to guide you through what you need and how to do it yourself? For safety's sake is the house end of the cable removed from the CU so that you would not be working near anything live?
The usual knowledge and helpfulness from Marconi, mixed in with a slight hint of violence ?
Be interested to see how this works out.
My concerns with the Varley Loop / Murry loop sort of tests here is the need for high current / low resistance adjustments. With ~25m of 16mm copper the total resistance of each conductor is of the order of 0.03ohms and you will struggle to find rheostats of that sort of value and ~10A rating just sitting around.
My approach is really a "Wheatstone Bridge" arrangement but instead of using the other arms to null (zero) a galvanometer, today we just use a decent DMM that will be > 1M impedance so can be ignored and if 1mV resolution for the meter we can get a meaningful reading / distance resolution with only a 100mV or so total volt drop. The balancing arm ratio then becomes maths on the two measured voltages.
So then test currents of the order of 5A are feasible and sustainable without worrying too much about how to get that much current (mid-size laboratory PSU, car battery with some current-limiting load like a 60W bulb, etc).
3. LAP AC/DC Digital Multimeter 600V - https://www.screwfix.com/p/lap-ac-dc-digital-multimeter-600v/161fg that's the multimeter I got but when I tried to measure resistance across the live and armour it just read "ERR". Nothing in the manual about how or why that can happen...
The Screwfix site lacks detailed specifications, such as the voltage ranges/resolutions supported. At least it is CAT-II rated, but that is not quite enough if measuring at the CU (instead of at the appliance after 13A fuse, etc) See:
The usual reason for getting an error when attempting to measure resistance is it is seeing some residual voltage there. It could be the fault is intermittent so only manifesting at higher test voltages so it is picking up capacitively coupled voltages, or it could be there is a small AC voltage of the order of 0.1V or so induced from some other energised circuit or current flowing back via earthed metalwork in the garage, etc.
As general advice, always check for voltage before you measure for resistance! Multimeters are not considered safe for "proving dead" as there are so many ways you can get it wrong, possibly resulting in a fatal shock if you failed to detect high voltages, or an inadequately rated meter exploding if subject to a very high energy fault.
That is what the likes of GS38 health & safety advice call for the use of a dedicated voltage tester, along with some means of proving it is working before and after you checked for the presence of high voltages. This is the sort of thing you would be looking at for a low budget:
The proving units are significantly more expensive (in the £70++ range) but for occasional use you can check it works on a circuit you did not switch off before/after you test one you plan on working on.
@danielz000 if marconi is offering to come and help, I would jump at the chance. His Knowledge is vast. You may not understand a 100% of what he is explaining to you though ?.
Ps.. I love @Lucien Nunes explanation of why a standard resistance test from each end may well not work! (i.e pin hole and filling channel tunnel). Really helps you see the problem, especially when you cannot understand all of the physics involved.
I might understand somewhere in the region of 5% on a good day (plenty of sleep and a decent meal the night before).
Hopefully the OP jumps at this chance and then reports back here on the experience.
If I'm interpreting it correctly the voltage drop (across R1+R2) is measured between the two ends of the faulty cable and then between one end of the faulty cable and the armour (just R1), one of the healthy cables is just being utilized as a 25 meter M.meter lead for the first reading. Not quite sure about the right calcs but assuming that the fault is say only 5 meters from the joined ends then the volt drop across RI might be V1x20/25. Would love to see actual test readings from this method.
I will do you a demo. All a bit academic now cos two joins underground not great future for this run of swa cable- one maybe tolerable but two …,…
I must have a go at that Varley test. I have a fault on a 4 core swa , 2 cores low resistance to each other and to earth. Would be cool to find the location of the fault, though most of the cable is now under a building extension. I do have a 20A variable PSU and some big resistors and power variable resistors
London
Buried SWA cable fault finding
danielz000,
marconi,