Scenario: Visibly burnt out, entirely blackened, ballast in a fluorescent fitting. Would this be noteworthy during an EICR and if so, how would it be coded? My thinking is that its an obvious fire risk.

Still an apprentice with millions to learn, any input would be appreciated.
 
Does the fitting comply with
416.2
Section 421
621.2(ii)
512.2
559.5.1
526.1

The internal section of the fitting is not part of the fixed wiring so unless any of the above are not complied with then its no code from me.
 
the fitting itself is outside your remit of testing to BS7671. as pp says. disconnect and no code. just tell customer if he wants to see where he's going , to replace fitting.
 
Read the definition below it?? An electrical installation is an assembly of electrical equipment. The lights clearly form part of the installation.
And which Reg number backs up the code? The regs only apply to the final connections carried out on site, cable entry in to the enclosure and the suitability of the enclosure.
 

Reply to Burnt out ballast EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Agree when you have a Senior Moment how is that still allowed, especially with all the regulations in place now, always a dangerous situation in...
Replies
12
Views
2K
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top