Hi all,

Hope someone can give me clarity around the need to bury an SWA cable please.

I've been asked to install an 4mm SWA from the main DB to a "to be built log cabin" at the end of the garden about 50m away, it will need to run along a fence for most the route (or underground).

I called NICEIC to clarify and they advised I cant clip it to the fence incase it falls down, cant leave it on the surface due to rodents and have to bury it for the entire length. My question is reg 522.8.10 says "burried cables shall be buried to a sufficient depth to avoid being damaged...." what do you guys call a sufficient depth and whats your thoughts about rodents chewing through SWA armour???

Basically what do you guys do in these cases??...

Many thanks,

M
 
See Attached, SWA Armor sheath is earthed at main board. The earth is isolated at outbuilding and eath rod installed to form a TT system with a 30ma RCD covering outbuilding. The supply to SWA cable feeding outbuilding should be protected by a time delayed RCD 100ma
there is a lot on the web about not exporting PME.
 
See Attached, SWA Armor sheath is earthed at main board. The earth is isolated at outbuilding and eath rod installed to form a TT system with a 30ma RCD covering outbuilding. The supply to SWA cable feeding outbuilding should be protected by a time delayed RCD 100ma
there is a lot on the web about not exporting PME.

That doesn't explain why though, you are just repeating a common misconception without backing it up with reference to the regulations or technical knowledge. Plus you've got it wrong, the SWA doesn't need RCD protection.

Creating a TT earthing system for the outbuilding is only necessary if there are extraneous conductive parts present in the outbuilding and if it is not practicable to install main bonding to them. At this stage in the OPs situation where they have not yet begun work the better options are adding a 10mm earth to the submain or increasing it to a 10mm 3 core SWA,this will give them a 10mm bond at the log cabin to connect to any extraneous conductive parts.

'TTing' as it has become known should be the last option considered as it swaps a very good, low impedance earth connection for what is likely to be a poor, high impedance earth connection. This then leads to a reliance on RCDs which are far from infallible.
 
Agreed however there are recommendations as attached document READ MORE HERE and you may need permission From DNO to export PME.

Think you're digging a trench for yourself here @Jeremy Hale :), that link is about using the armouring of swa as cpc.

If you look in the resourcing section, there's some content about this matter. I've read before about permissions from DNO's etc, but never found any such requirements. We have to abide by BS7671, they have other regulations.

 

Reply to Burried SWA for a log cabin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top