OP
Guest123
so does that mean you would use the max zs reading of the breaker for the design???? sorry
No, the permitted device Zs doesn't come into the equation. The value used is the calculated theoretical of circuit Zs found by using the formula Zs = Ze+(R1+R2).
This theoretical Zs value is then used in a calc with the supply voltage to find the (I) component (which is the maximum earth fault current that could flow in a fault condition) of the adiabatic equation which is - S = sqroot of I squared x t divided by k.
The use of this equation with the correct information will then confirm wether or not the CPC of the proposed circuit is large enough to cope with the fault current that may flow in it.
Last edited by a moderator: