As far as I am aware, the ESQCR prohibits the use of TN-C within an installation connected to the public network.
As such any connection to the PEN conductor is made outside of the installation.
 
If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.
 
Reg 705.411.4 says a tnc shall not be used. Other words a PEN conductor cannot be used. Meaning seperate earth shall be used, example tt sytem.
You are not using TN-C because the neutral and cpc are separate through the consumers installation.
 
If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.
I see where your coming from but lets say you loose your pen conductor at the very source from the transformer. Not at the point at which you make it a tncs when connecting your earth. But the very source. If that pen conductor goes down, where is your mean of earth?
 
No you cannot use a PEN conductor, just the same as you cannot use a PEN conductor in your house.
Doesn’t necessarily mean TT is the only option.

What really matters, is whether PME can be used.
In some circumstances it can be used, though it would be advisable to install an earthed metallic grid in the ground where livestock are to be kept.
 
No you cannot use a PEN conductor, just the same as you cannot use a PEN conductor in your house.
Doesn’t necessarily mean TT is the only option.

What really matters, is whether PME can be used.
In some circumstances it can be used, though it would be advisable to install an earthed metallic grid in the ground where livestock are to be kept.
I agree PME is the way to go, like you say especially if livestock can come into contact with the installation
 

Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top