Cable calculation | Page 3 | on ElectriciansForums
Discuss Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net
No but in terms of over current in a domestic dwelling ive seen a db have 100amp main switchbwith and the main head bein 60amp fuse, the fuse in the main head would blow before rhe main switch would trip. Which is incorrect but why is this done.
I think this is the clincher. Get someone competent on this job mate.
So why is this done out there, having main switch on the board rated higher than the fise in the head, it dont make sense the fuse in the head would alway blow first.
Do you not think it a good idea to have a switch rated equal or higher to the current that could be drawn through it?
Under the Electricity safety, quality and continuity regulations 2002 you cannot use a suppliers earth to an out building, on a TNC-S Earthing arrangement, so the detached garage effectively becomes a TT installation with an earth electrode installed in the ground.
Ok lets say you exported the earth on a tncs to an outbuilding, and then lets say you lost your neutral at the main incoming, if you had a live to earth or neutral short, every thing connected to earth would become live under fault conditions, hence why you need to rod and not export form the main earth to exterior building ect
There are a couple of reasons why you would not export a PME earth.
One could be if the exterior of the outbuilding is metal, and the other is if there are extraneous conductive-parts which would require bonding.
At the end of the day, it boils down to cost.
Is it cheaper to run a 3 core 10mm2 armour or a 2 core armour and install an earth rod.
Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...