Cable calculation | Page 4 | on ElectriciansForums
Discuss Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net
Ok lets say you exported the earth on a tncs to an outbuilding, and then lets say you lost your neutral at the main incoming, if you had a live to earth or neutral short, every thing connected to earth would become live under fault conditions, hence why you need to rod and not export form the main earth to exterior building ect
So why is it matter if it is an outbuilding or not? That would still happen in a building that is not an outbuilding.
You are incorrect.
Section 705
705.411.4
Read that little paragraph mate, starts with tncs shall not be used.
I dont make the regs, it was a question i had of the nic eic on the onsite assessment
A TN-C system has a combined neutral/earth on the service side and throughout the consumers installation, very unusual.
Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...