If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.

A picture to help you.

[ElectriciansForums.net] Cable calculation
 
You are not using TN-C because the neutral and cpc are separate through the consumers installation.

The third letter means how the earth and neutral are linked at the transformer.

T = earth
N = Neutral
C = Combined.

This is true of both a TN-C and a TN-C-S. the S is for ‘seperate’ as the earth is then seperated from the neutral within the installation.
 
Il give you the scenario, stables in a field, e-on have been out and put a supply in a hut with a meter on and a one shot, main fuse is 80amps, the customer need a fuseboard putting in the barn, 75metres away, what size cable would i be looking at, ive done a calculation, 1 x swa cable 3 core, burried, ive use 80amp as the demand as this is the maximum at the origin and the cable size is coming back at 25mm. Is the right or is there some sort of diversity applied which would allow you todrop to 16mm. All that will be going in are sockets and light, quite a few to be fair but altimatley just wanted to get the armoures cable to the fuseboard and just questioning the size. Any help is appreciated
 

Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top