Chris Electron

Hello,

Can anyone tell me please if you can use the figures given in BS7671 cable current carrying capacity when using 12V?

eg- so 1.5 multicore clipped direct can take 19.5A. Is this what the cable can carry for both 12V and 230V- or any other voltage?


Any help greatly appreciated!

Thanks,

Chris.
 
Weard, but i have forgot the maths to work out Amps im using a 50v Lighting system and cable is 2.5 not the usual 1.5 as amps are more in this system...

Hope to see some great reminder Calcs here plz not done them for years...
 
Thank you for this. I find it hard thinking that amps at both 12v and 230v are the same thing. If you grabbed hold of a cable with 12v and say 10A running through it you would live to tell the tale. But not 230V.
 
My palms have enough resistance to withhold a ELV pd, but 230 will just jump on in there! 0nce it gets through the difficult bit ( the old calloused skin), the wet fleshy bit isn't so resistive and just lets it flow (man!) Current will kill you, but only if it can get in there. Enough rubber, or any other insulator, will inhibit the path, a Faraday cage gives it an alternative path
 
Thank you for this. I find it hard thinking that amps at both 12v and 230v are the same thing. If you grabbed hold of a cable with 12v and say 10A running through it you would live to tell the tale. But not 230V.

It's irrelevent what current the cable is carrying. Your body has a certain resistance, 12v at your finger tip will produce 20x less current flow through your bits and pieces than that of a 240v pd (and we all know that it's the current that will fry you). Simple ohms law.
 
Chris - If you where hit by a lorry, the amount of damage caused (power transfered) would be a result of both the size and speed of of the vehicle. Think size is the current in amps and speed the voltage. The product of these would be the energy/power transfered measured in watts. Hence

Power(watts) = Current (amps) x Voltage (volts).

A basic calculation to derive the amount of current a load draws would see this formula swapped round to

Current drawn = Power/Voltage
 
As RT illustrates above, this is why power line transmission voltages are high.

The power lost across the length of a power line is equal to the square of the current carried multiplied by the cable resistance or

P=I2R

As the cable resistance is fixed higher voltages are used to transmit the same power at a lower current to limit the power lost across the line.
 
Put some
Figures in that equation and see the difference

100 watts/12 volts = 8.33 amps

100 watts/230 volts = 0.43 amps

100 watts/130 000 volts = 0.0008 amps

Haha!! reminds me of the numerous times i've seen drawings for swimming pool lighting with wiring sizes totally inadequate for the load and distance. 2 X 300W/12V lamps these pools usually take, so drawing around 25A a piece. ...lol!! Often seen cable sized at 1.5 / 2.5mm, obviously a junior at work, forgetting they are 12V when doing his calculations...lol!!
 
Don't forget to calculate the Zs for MCB's ect using the new voltage, not 230.

As E54 and others have mentioned, the current draw of the load should be calculated using the applicable voltage, and this is then compared to the BS7671 tables, once installation derating factors are taken into account.
You should then check volt drop. In ELV installations, volt drop and Zs are the prime constraints on cable size.
 

Reply to Cable Capacity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top