I would just put a steel 25mm conduit with endbox behind consumer unit straight up into the loft in the corner if you can (im asumeing con unit would be in a corner), then you can pull in what you want at later date.

On the timber frame houses we do we stick a 25mm plastic conduit straight to loft for solar at later date, and its behind the stud work so it will be 125mm back from the surface too.

I would advise however to install inverter else where, im not keen on installing them in lofts although many do.
 
SWA may not be regarded as sufficient protection against nails and the like if burried in a wall less than 50mm. neither is metal capping.
 
No, you're right Gavin, never on a shared RCD. Most TL manufacturers will tell you that their unit exhibits about 20mA AC leakage under normal operating conditions. Odd though, that SMA "recommend" a 100mA min trip limit (to avoid nuisance tripping) and I could be mistaken but didn't P1 always recommend a 300mA trip limit, per inverter - although that could be due to the fact that most of mainland Europe (especially Germany curiously) don't consider a 100mA trip limit RCD as a standard rating, normally using either 30mA or 300mA.

So, we know in practice that a 30mA limit on a dedicated circuit is generally ok with a good quality TL unit (damp mornings are when a problem will typically materialise as we know) but on the other hand we have manufacturer's recommendations to follow....what to do? ;-)

which is why I didn't understand your previous post! Hence Huh!
 

Reply to Cable from loft to CU in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
216
Sounds more positive.
Replies
8
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top