cliffed
What’s your thoughts on this, house testing I would say no argument against this, mains isolation & tests can be carried out.
Commercial properties where isolation is not possible i certainly would not do a R1+R2 test, also knowing the EOL near impossible.
Electrician’s are now deducting the Ze from their Zs & putting this on the cert, its so blatant & obvious, why are they even doing that.
It’s similar to “Fudging” Insulation Resistance measurements.
I certainly if required would do a R2 test, but this seems a No, No, amongst shall I say younger Sparkies.
During a EICR there is no requirement to do the R1+ R2