Hello
Looking for some guidance please.
Lived in current house just over a year now and had couple issues with our pull cord switch (45A) sticking. Also at its worst, experienced the neutral burnt out.
My relative (industrial electrician) has put some potential issues across to me so was hoping you could all help make sense of it all.
Shower is 9.5KW
Unsure on voltage 230/240
Cable is 6mm
MCB is 32A type 2.
Cable from consumer to pull cord no more than 10M inside wall.
Pull cord to shower 1-2M above ceiling.

They have put doubts to me that the cable may not be big enough
Other option is they said to get smaller shower.
 
BOLLOX 2 U... 9.5kW/230V=41.3A
if you read Linksy5 comment Cables buried in wall not clipped direct
Surely you know about voltage drop

Technically you are correct, if this was being wired from scratch a 10mm/45a circuit would be installed. However the OP is simply complaining of pullswitches failing due to thermal damage. That will be nothing to do with the cable size or mcb rating and everything to do with poor connections at the switch.
Given the short duration of the load for a shower it's unlikely that the 6.0mm and 32a mcb will ever be a problem , the issue is poorly connected pullswitches and rewiring the circuit will not resolve that..
 

Reply to Cable size issue with size of shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top