Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
It does feel like I'm doing more than I should if you know what I mean, think about it, why am I bothered about the installation and esrthing that when that's already got a perfectly good earth.

I I feel if I put a charger in, with an additional rod, I've done my bit, then in the event of a fault where you loose the neutral, it's there as a fail safe / backup.

You are bothered about the installation because you are trying to comply with that (ii) option for connecting to the PME earth.

If you don't want to do that then obviously you can just not connect it to the PME earth and set up you own earth system just for the charging point, but you will then have to make sure that all metalwork connected to it is suitably far away from any bonded to the PME earth and also that the electrode's zones of influence don't overlap with those created by any buried steelwork bonded to the PME earth.
 
I can see your point with this, but what are the chances that the building is going to be so far out of balance that the neutral current is going to be that great?

Maybe not at the moment it isn't, but I seem recall Tony of this parish had overheating Bonding conductors, and I don't fully trust BS951 clamps, or plumbers replacing them either properly or at all ;-) plus if you are going to all this bother in the first place why not ? it would not cost that much more in the scheme of things now that we are trying to achieve sub ohm TT rod nests, just my opinion of course
 
I could take a 10mm back to the met, it's about 16 meters so not going to cost the earth, just strap it to the side of the swa.

I suppose when it gets outside, I'll just tie it to the tray, but it's not exactly uv resistant is it not should be outside unprotected like that, so that then creates yet mother sodding problem.
 
Yeah I looked at that in Amd 2 Archy,
My only niggle with that is if it can be guaranteed , plus I as trying to be constructive with all of the methods available :)

To throw another grenade a 1:1 isolation transformer is yet another available method ;)

Good discussion a lot better than " my RCD is tripping help!" threads :)
 
I could take a 10mm back to the met, it's about 16 meters so not going to cost the earth, just strap it to the side of the swa.

I suppose when it gets outside, I'll just tie it to the tray, but it's not exactly uv resistant is it not should be outside unprotected like that, so that then creates yet mother sodding problem.
stick it in copex
 
I could take a 10mm back to the met, it's about 16 meters so not going to cost the earth, just strap it to the side of the swa.

I suppose when it gets outside, I'll just tie it to the tray, but it's not exactly uv resistant is it not should be outside unprotected like that, so that then creates yet mother sodding problem.

16mm can be buried direct ;)
 
Yeah I looked at that in Amd 2 Archy,
My only niggle with that is if it can be guaranteed , plus I as trying to be constructive with all of the methods available :)

To throw another grenade a 1:1 isolation transformer is yet another available method ;)

Good discussion a lot better than " my RCD is tripping help!" threads :)

i think because it is not in everyone's everyday workload list everyone is listening to everyone else. Very good thread.
 
Yeah I looked at that in Amd 2 Archy,
My only niggle with that is if it can be guaranteed , plus I as trying to be constructive with all of the methods available :)

To throw another grenade a 1:1 isolation transformer is yet another available method ;)

Good discussion a lot better than " my RCD is tripping help!" threads :)

The transformer idea could be an idea, but I think I'll stay away from that one as I've already agreed a price and don't want to go too far astray, I'm still well in acceptable.

Yeah it's a good thread, it's nice that it's not been ripped apart, I thnk we have all have valid points and probably all had differing views.
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
346
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top