Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
Maybe not at the moment it isn't, but I seem recall Tony of this parish had overheating Bonding conductors, and I don't fully trust BS951 clamps, or plumbers replacing them either properly or at all ;-) plus if you are going to all this bother in the first place why not ? it would not cost that much more in the scheme of things now that we are trying to achieve sub ohm TT rod nests, just my opinion of course

Not at the moment? its going to have to be a long way out of balance to get a neutral current large enough to bother 10mm.

I'm not disagreeing with you and do agree that your suggestion of 16mm is a better idea. Just wondering how much neutral current there will ever be in the installation, seeing as it is three phase and the phases should be well balanced as its a new install.
 
Just wondering how much neutral current there will ever be in the installation, seeing as it is three phase and the phases should be well balanced as its a new install.



It depends partly on where on the DNO network the neutral break occurs and whether other customers are also affected.

In theory there should be multiple earth rods along the CNE to limit the problem.
 
Last edited:
Not at the moment? its going to have to be a long way out of balance to get a neutral current large enough to bother 10mm.

I'm not disagreeing with you and do agree that your suggestion of 16mm is a better idea. Just wondering how much neutral current there will ever be in the installation, seeing as it is three phase and the phases should be well balanced as its a new install.

Triplens ?

In all honesty I don't even know what the building is used for ;) not disagreeing either just a good discussion, and interesting
 
It depends partly on where on the DNO network the neutral break occurs and whether other customers are also affected.

In theory there should be multiple earth rods along the CNE to limit the problem.

The idea of having an earth nest connected to the MET is that you have a connection to earth under your control and so that you are protected against breaks in the CNE conductor between your installation and all of the DNO earth rods
 
The idea of having an earth nest connected to the MET is that you have a connection to earth under your control and so that you are protected against breaks in the CNE conductor between your installation and all of the DNO earth rods
Yes, totally agree with your thinking Dave.

Sorry, my post related to the potential magnitude of a CNE failure without any customer installed rods etc.
 
Triplens ?

In all honesty I don't even know what the building is used for ;) not disagreeing either just a good discussion, and interesting

Ah yes, the good old harmonic problem, that does put another spin on it.

If I was doing this I would have been looking at at least 2 earth electrodes each with a seperate 10mm back to the MET, so in theory under a lost neutral connection the neutral current would divide between the 2(or more) rods (assuming similar Ra for each rod)
 
Ah yes, the good old harmonic problem, that does put another spin on it.

If I was doing this I would have been looking at at least 2 earth electrodes each with a seperate 10mm back to the MET, so in theory under a lost neutral connection the neutral current would divide between the 2(or more) rods (assuming similar Ra for each rod)

Ah! that is where my thinking slightly differed, I was thinking of linking all the rods together locally with a single cable back to the MET, I was also expecting maybe 4 rods or more to get a low enough Ra, soil type dependent of course
 
Ah! that is where my thinking slightly differed, I was thinking of linking all the rods together locally with a single cable back to the MET, I was also expecting maybe 4 rods or more to get a low enough Ra, soil type dependent of course
If you decide to connect the rods directly to the MET, bear in mind that they don't need to all be right next to the car charging point. It might give you easier cable runs.
 
Ah! that is where my thinking slightly differed, I was thinking of linking all the rods together locally with a single cable back to the MET, I was also expecting maybe 4 rods or more to get a low enough Ra, soil type dependent of course

4 rods? I'm not suggesting for one min this is going to be acceptable, but sub 200 ohms is deemed as stable, so it would be easy to satisfy that requirement, but it's satisfying the other part of the equation.
 
If you decide to connect the rods directly to the MET, bear in mind that they don't need to all be right next to the car charging point. It might give you easier cable runs.

The OP was planning on putting the rods close to the EVC to keep the cabling simpler, I was just rolling with that as he knows the site and I don't ;)
 
Last edited:
4 rods? I'm not suggesting for one min this is going to be acceptable, but sub 200 ohms is deemed as stable, so it would be easy to satisfy that requirement, but it's satisfying the other part of the equation.

Not for your purposes 200 ohms is anywhere near acceptable, we are aiming for about 1 ohm if not lower lol have you looked at the calc Richard Burns did on the other thread you posted earlier ? we are not talking about TT here
 
How do you know one rod will not be enough?

Unless you are specially ordering 8' rods from someone like furse then you'll be using the same 4' long rods we all use no? A single 4' long rod will not provide a stable resistance to earth, you'll need at least 8' depth to get stability so will need at least 2 joined (i recommend solder/braze the joint to stop it rattling loose when you wallop it in)

Add to this I have never yet managed to get a single figure Ra with a single rod, and even if I did I wouldn't trust that to remain stable.
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
346
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top