Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
it is a bit more than that, there are rules specifically for PME, you need to follow these, if TSHTF it will be you in deep doo doo
I'll admit my lack of experience for vehicle charger installations, but what exactly is the danger here? There's an external socket that connects to the charger unit in the car which I assume is double insulated.

I know there are specific regulations about this application and that I haven't fully read them, but why is this anymore likely to harm anyone than mowing the grass with a Flymo?

Personally, I think the greatest risk would be to solely TT the charger socket if it can be simultaneously touched with the steel building cladding which is connected to the PME terminal.
 
Don't forget when doing the calcs to add the new chargers load to whichever phase, if you can comply with exemption I) then it don't really matter about the Ra of the steelwork, you have already complied with BS7671, if the steelwork has a fortuitous low Ra then great
 
I'll admit my lack of experience for vehicle charger installations, but what exactly is the danger here? There's an external socket that connects to the charger unit in the car which I assume is double insulated.

I know there are specific regulations about this application and that I haven't fully read them, but why is this anymore likely to harm anyone than mowing the grass with a Flymo?

Personally, I think the greatest risk would be to solely TT the charger socket if it can be simultaneously touched with the steel building cladding which is connected to the PME terminal.

The main concern as always is a broken suppliers N, where anything connected to the local CNE link can rise to phase voltage, read the caravan/marina regs :)
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)

I feel we might be being ignored here a smidge! :)
But having now seen some loading figures, I reckon your suggestion of the isolating tranny is by far the best solution!
 
The main concern as always is a broken suppliers N, where anything connected to the local CNE link can rise to phase voltage, read the caravan/marina regs :)
Thanks Spark 68.

I totally agree with what you are saying, but the only additional risk is surely the metallic enclosure for the car charger sockets.

In the case of marinas and caravan parks there is little control over the use of the sockets and the combination of bare feet and extension leads/home built electrics. With this car charging installation the cars are likely to be connected with purpose made leads and the charger units in the cars most likely double insulated.

I'm not questioning the regs, just trying to understand the background thinking behind them.
 
Thanks Spark 68.

I totally agree with what you are saying, but the only additional risk is surely the metallic enclosure for the car charger sockets.

In the case of marinas and caravan parks there is little control over the use of the sockets and the combination of bare feet and extension leads/home built electrics. With this car charging installation the cars are likely to be connected with purpose made leads and the charger units in the cars most likely double insulated.

I'm not questioning the regs, just trying to understand the background thinking behind them.


In the event of a broken suppliers N (on PME) and Depending on the EVC the metalwork may become live, either the charger itself, or depending on mode possibly the vehicle itself (live DC ?), else why would they have all of these regs associated ?

I was in a IET seminar before AMD2 and originally (allegedly) the IET did not want PME connected to these chargers at all!, then there was argy bargy about the vehicle connection socket allegedly, I don't know if some of the decisions we ended up with were political at EU level rather than technical or what, then we had AMD2 ;)
 
Ok but how would you actually test the steel structure, it will not be possibles to guarantee that the water service is 100% disconnected and you are only testing steel as probably cannot access every single part.
what would you do? Disconnect the main earth and try doing a Ze to the steel bond?

Can't think of any other way to test the steel structure....
 
Ill be honest, I am looking at this in two ways, on one hand I accept and agree with what you are saying, but on the other, I feel its making a mountain out of a mole hill.

I really do not know what to do now.

Welcome to been the boss and having peoples safety come first.. Its a crap club really but with up's & downs on the way, chin up:smiley2:
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
346
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top