Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
Well I called the NICEIC today and they said do not put an earth rod in and just take the SWA out the building and make it part of the TN-C-S installation.

I explained everything in full and explained the proximity to the building etc and that the building it metal and so on.

They even emailed me to confirm as I asked them, they said its fine, they said that in reality its never ever going to be a problem.

So, will the judge accept 'the NIC said it's ok' in preference to 'I followed bs7671 to the letter' ?
 
so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)

The problem here was the proximity of the PME bonded metal clad building to the TTd ECV, you would be able to touch both Earthing systems simultaneously, which is a shock hazard due to true Earth of the TT part relative to the PME part which may not be at true earth potential at any given time.
 
They said the three phase part for section (i) and also the fact that its a steel building with the steel bonded, he said thats more than likely better than any rod you will put in.

More than likely better? That's a very precise and technical response!

Once you've tested the effectiveness of the steel structure as an earth then you will be better informed about this. Then with test results to prove it you could make the informed decision that this is safe to do.
 
More than likely better? That's a very precise and technical response!

Once you've tested the effectiveness of the steel structure as an earth then you will be better informed about this. Then with test results to prove it you could make the informed decision that this is safe to do.

What would the best bethod be to achieve this on this type of buliding?
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)

He's adding a 60A single phase load to the system, so unless the system is 60A out of balance then the system will be thrown out of balance when the charger is in use.

Clamping it will only give a brief snapshot of the loading, a couple of weeks load study would really be needed to establish a proper idea of what the loading is like.
 
He's adding a 60A single phase load to the system, so unless the system is 60A out of balance then the system will be thrown out of balance when the charger is in use.

Clamping it will only give a brief snapshot of the loading, a couple of weeks load study would really be needed to establish a proper idea of what the loading is like.

I thought he was fitting a 3 phase charger ?

Agree that longer term monitoring would be a better bet, but if it is outside of the parameters of exemption I) to begin with then he is going to have to load balance it better to start with no?
 
Yes they have two cars already that both draw 16A so that's 32A straight off.

I think without looking at my notes it was 8A on L1, about 30A on L2 and 8A on L3

I am going to put this on L1.

Im not being funny but nobody is ever going to monitor this for even a day let alone two weeks.
 
I thought he was fitting a 3 phase charger ?

Agree that longer term monitoring would be a better bet, but if it is outside of the parameters of exemption I) to begin with then he is going to have to load balance it better to start with no?

I was toying with the idea but it was a non starter after discussing it with the manufacturer due to various reasons with the charge point.
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)

Ok but how would you actually test the steel structure, it will not be possibles to guarantee that the water service is 100% disconnected and you are only testing steel as probably cannot access every single part.
what would you do? Disconnect the main earth and try doing a Ze to the steel bond?
 
My main point still stands, look closely at the formula in the associated annexe to exemption I) to see if you can get within the paramaters, you may have to juggle the loading about a bit, this is a starting point
 
You don't have to sit there logging it in person, a data logger does that for you and you download the data to your pc.

I appreciate that, but it seems like we are all going a bit over the top, this is just a car charger thats being installed, it's no more than a glorified weatherproof socket on the side of the building.
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
346
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top