Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
I really do appreciate Kate all your help and constructive feedback on this, it's an area that itself has had the regs fiddled with and also other issues like earth rods and distances to the building.

Ok so if we break it down into small chunks, let's hypothetically say we will go with the earth rod, it says connect it be k to the met. Do we have any information anywhere as to what reading is acceptable that we must achieve?


Top op of head moment:

take a 2 core SWA cable from the internal dist board using the sheath for the earth

terminate into a plastic isolator externally and RCD at this point

take another SWA from the isolator and run the cable underground to the new VCP.

Install this at least 2M from the metal building

earth the underground SWA sheath and the VCP by an earth rod and earth pit.

Test
 
it is a minefield eh?

It it is unusual for DNOs to provide earths to metal framed building is it not?

This is job may need a step back and reasses. Many heads are better than one.

Quite a few years ago I was part of a crew of agency sparks working on a new agricultural building being built on a farm, we were mainly responsible for installing the services in the building (lighting and power), another crew were sorting the supply to this building including the Earthing segregation from the main intake (PME) and installing the TT parts and all ground works.

The DNO were involved due to an upgrade of the supply for the increased demand.

Anyway to cut a long story short the DNO were unhappy about the proximity of this new metal clad TT building and extraneous parts of the PME bits, I don't know what the final outcome was as we were finished our contract, but I do know there was hell to pay at the time.
 
Top op of head moment:

take a 2 core SWA cable from the internal dist board using the sheath for the earth

terminate into a plastic isolator externally and RCD at this point

take another SWA from the isolator and run the cable underground to the new VCP.

Install this at least 2M from the metal building

earth the underground SWA sheath and the VCP by an earth rod and earth pit.

Test

i like the idea but there just isn't the option to do this unfortunately due to it being a car park immediately outside the building.
 
Quite a few years ago I was part of a crew of agency sparks working on a new agricultural building being built on a farm, we were mainly responsible for installing the services in the building (lighting and power), another crew were sorting the supply to this building including the Earthing segregation from the main intake (PME) and installing the TT parts and all ground works.

The DNO were involved due to an upgrade of the supply for the increased demand.

Anyway to cut a long story short the DNO were unhappy about the proximity of this new metal clad TT building and extraneous parts of the PME bits, I don't know what the final outcome was as we were finished our contract, but I do know there was hell to pay at the time.

I seem to think this is going to be more problematic than planned for.

i think other than connecting the rod to the met there's probably not a lot of choice.
 
Even if it is PME you may well find there are earth rods already fitted, a lot of newer PME industrial units have earth rods fitted, a look around the perimeter of the building often you will see the inspection pits
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
348
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top