hi in collage today we were doing cable sizes and i am stuk on one question can any one help.
the question is
the load is 50Kw
3phase
the total lengh is 50m
its ran in metal trunking with 1 other circuit
30 degrees room temp
what will be the cablke size required and what mcb should be used?
i have had a look and i think it should be 16mm 5core and 125A mcb but i think im mising some thing. any one help
It does, not being awkward but if you get the answer without knowing how you got there its is about as much use as a choclate teapot
could you talk me through it step by step? its only the 3rd Q i have done on them only trying to learn and get my head around it, maybe it was a fluke lol
50kw/415= Ib 121A (Design current)
In= 125A (mcb)
125/.80= 157A what your cable should carry
It, tabulated current says you should go with 95mm squared
volt drop= 0.48(mV/A/m) x 121(Ib) x 50(length)/1000=2.9V
thats what i get,maybe make some sence to you
Reply to cable sizes in the Talk Electrician area at ElectriciansForums.net
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...