remember voltage is 400V so can expect to get considerably more power and 3x that because there are 3 phases :)

You would also see if Vd was ok using Vd = Ib x Length x mV/A/M (value found from table 6D2) it turn out ok - well less than 5%

These lecturers always keep the really tough questions til last means they won'tbe stuck withnothing to do at the end of the lesson ;)

hope i've been some help and not made some stupid mistake somewhere.
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.

I wouldn't bet my life on me :D but your 217A figure comes from using 230 volts! It is 3 phase so you should use 400V and root 3
 
so how would the lay out work? i take it its just ran out the CU

you have been a great help thank you very much


probs to an isolator then to the motor - remember there is an mcb for each phase and if it is a motor they won't be type Bs

you still not seeing that button lol
 
brain in gear (just)

50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)

correct and then share between 3 phases.

Edit: on reflection think your 72A is Il (line current) as the formula is for total power! so factors and mcbs should be done on that figure oops!
 
Last edited by a moderator:

Reply to cable sizes in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
476
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top