fivestar

I am carrying out a major re-wire on a farmhouse which is also having a substantial extension. Can I run the t & e cables for the socket outlets on top of the concrete subfloor - they will be protected by the kingspan insulation from the floor screed when it is poured and as they are in contact with the ground directly should not be a problem with heat.
 
First you need to your cable calc's with regards to thermal effect , then consider using conduit, I would never screed over unprotected T & E
 
Why not run them in conduit directly on the concrete floor membrane
When they are inbedded in the concrete there will be plenty of protection and an air gap through the pipework
 
whenever ive put t+e under concrete to get to kitchen islands or for in floor lighting etc ive put it either in conduit or trunking be swayed more towards the trunking as its bigger and helps with thermal effects etc for your cable calcs
 
I use Kopex much better for laying around the perimeter of the room and around corners. I cut the Kopex to length and then pre wire it, then usually use raw plug cable tie eyelets and then cable tie the Kopex to the concrete sub-base and then the builder screeds over it.
 
Last edited by a moderator:
Lovely bit of conduit there Pennywise, did you do the bends with a spring or buy pre fabricated ones? What is the long rectangular thing in the middle of the wall?
 
Spirit level i reckon, i've heard about them but never seen one in real life.
its up there with them fancy dustpan and brushes you can get (google it if your not sure);)
 
Spring it's far cheaper, and the bit in the middle is 2 by 2 trunking for the plasma screens cables.
 
Last edited by a moderator:

Reply to Cables in concrete floor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Article
This is an RSS feed of thread: Hole in copper pipe, solder under floor, T coupling & protection Content of the thread: I was stupid enough not to...
Replies
0
Views
202
  • Question
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about...
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top