Calculating inverter for motor | on ElectriciansForums
Discuss Calculating inverter for motor in the UK Electrical Forum area at ElectriciansForums.net
Q
Quang_Lo
Dear All,
I have a problem. It's calculating inverter for 3 pharse non-synchronous. I mean that i don't know the formula. My colleagues show
Here we go :
P[SUB]1[/SUB]/P[SUB]2[/SUB] = (n[SUB]1[/SUB]/n[SUB]2[/SUB])[SUP]3
[/SUP]Please help me out
Dear All,
Here we go :
Rate the inverter for the motor being used.
It really is that simple.
The only real effect on a drive with cable length is if it needs line filters for EMC compliance. Otherwise as Besoeker has stated, match the dive for the motor size.
Most drives will have 2 ratings heavy duty and normal duty, pick which is suitable.
Cable size is then specified using the normal methods.
Currently commissioning an MCC fitted with ABB ACS 800 drives, some of which ABB oversized wrt motor rating plate because of long cable runs.
Motors with excessive torque demand on ramping start/stop set-ups may require larger inverters to avoid shock load tripping issues, I know 2 brands that recommend this, also excessive start/stop duty may warrant a larger inverter too.
2 reasons off the top of my head for getting larger inverters than motor rating.
Occasionally our choice of inverter will be driven by a requirement for a wider range of carrier frequencies than normal.
Frequency of stop/start cycling would be an issue that we'd address with uprated forced ventilation rather than oversizing.
Don't understand how you would get excessive start up current with a correctly designed and set up system.
Not saying you cannot, but just cannot see it in my experience of moving heavy loads with VSD's.
Reply to Calculating inverter for motor in the UK Electrical Forum area at ElectriciansForums.net
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...