dont work like like that, too many unknown extra resistances in switches and terminations that will not be included in your calcs

your observation whilst partly true, is irrelevant. Zs can be obtained by calculation or measurement. The title of this thread is 'Calculating Zs with only R2 reading'.

You can't let your opinions cast a shadow over the facts.
 
One cannot calculate Zs when all one knows is Ze and R2, unless you can be certain of the R1/R2 ratio for the circuit (eg a 6/2.5 radial supplying a cooker).
However, for other circuit types you can estimate Zs. For lighting circuits and heating control circuits I generally estimate Zs = Ze + 3R2. I also state on any report or cert that this is an estimate.
Usually though, the purpose of measuring R2 is to prove cpc continuity and calculating or estimating Zs from this is unnecessary.
 
sooooo no it cant be done and or yes it can b

the reason i ask is did a periodic today and only did r2 on lighting circuits. Dont like doing zs on lighting points as i dont like live testing from high up on a ladder
 

Reply to calculating Zs with only R2 reading in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top