Discuss Can anyone help with my bathroom light pull chord switch? in the Lighting Forum area at ElectriciansForums.net

Joined
Oct 13, 2022
Messages
20
Reaction score
0
Location
Upton
I’ve got my P16th edition papers in 2006 so not a total beginner (I’m plumber as my trade tbh) but this pull chord bathroom light is not working and if trips the consumer unit .

Basically the old switch broke so I took a photo of the wiring before fitting a new light.

And it doesn’t work.

The brown an red wires are live and the two connect together are live too. I test them with this blue pen tester .

I’m gonna include photos of everything so any help be great thx
 
TL;DR
I know what I’m doing but basically I’ve no idea what to do here. I’ve just copied what was there before

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    362.2 KB · Views: 39
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4130C53C-8A03-426D-8263-9CE4ACF0C088.jpeg
    408.8 KB · Views: 31
  • IMG_7254.MOV
    4.6 MB
  • IMG_7255.MOV
    14.6 MB
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4718D26D-FFEC-473F-A58D-2F3949F94275.jpeg
    408.8 KB · Views: 32
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    1A3B9300-6B5C-477B-ABED-6DAC4415246E.jpeg
    350.7 KB · Views: 35
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    5F1F3656-4B2C-463A-BB7D-6379D6B21998.jpeg
    419.9 KB · Views: 35
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    690.5 KB · Views: 33
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    353.3 KB · Views: 27
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    0A51F626-B8EB-43C0-A335-3A621B71B4C9.jpeg
    350.7 KB · Views: 33
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?
Your old switch is two way, but it looks like only the two screws on the left side (third photo) have been used- I'm assuming there aren't enough wires for a two way circuit. Is there another switch for this circuit?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Also be wary of quirks of pen tester.
 
Last edited:
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Be wary of quirks of pen tester.
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
 
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
 
Last edited:
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
I’ll take some more photos and post them now
 
more photos
The trip switch is first one on the left
 

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    754A5946-9652-4825-BCDA-43586D96EBDB.jpeg
    335.2 KB · Views: 22
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    1D5A36DA-B2E6-46AF-8FE1-A2BFA965317E.jpeg
    348.3 KB · Views: 25
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    810DD0F0-ECD1-4B3E-AFC5-302D81459905.jpeg
    227 KB · Views: 22
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    3FDA34D8-9667-4184-811F-9967BAE6FE00.jpeg
    372.5 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    C10247E8-05C1-43DC-8E72-93C4A6A4CD4D.jpeg
    311.1 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    B5AF8C51-D4BF-4FDB-B6A1-30F8A824BDDE.jpeg
    388.2 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    03E319AF-B04F-45ED-9578-6F8AE1DAF593.jpeg
    372.5 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    49286AF6-E2A3-4BA8-84CB-84550E631299.jpeg
    311.1 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    DBF5529B-FC85-4ABB-8B45-66C28E63AEC4.jpeg
    227 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    6F9CCFF6-0A7D-4FE5-BC0B-07DA78749D73.jpeg
    345.9 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4784BC13-8DBF-48CB-AAA8-C25225F40637.jpeg
    324.2 KB · Views: 27
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
 
Last edited:
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
 
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
 
Last edited:
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
 
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
 
Last edited:
Please could you explain the series of events that lead to the breaker tripping?
Did it trip when you first turned the power back on after wiring the lights,
or did you switch the power on, nothing happened, then you pulled the switch cord, and the breaker tripped?
If the second, the pull switch might now be welded permanently on!

Normally one would expect to test a circuit before applying power to it, though that doesn't seem to be the DIY way!
 
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
 
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
OK I understand better, thanks.
It seems obvious to concentrate on there being something wrong in or around the new switch.
The way you've described wiring it is how I would have done it!

Do the lights work all of the time, and the mcb trips only sometimes, or how does the tripping manifest itself?
 

Reply to Can anyone help with my bathroom light pull chord switch? in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
469

Similar threads

Thank you, both. Seems like common sense may have prevailed, and the fellow is indeed going for one of the modern mirrors you mentioned...
Replies
3
Views
334
  • Question
"Value engineering."
2 3
Replies
39
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top