Can I use the sheath of the SWA as the CPC in this example? | Page 2 | on ElectriciansForums
Discuss Can I use the sheath of the SWA as the CPC in this example? in the UK Electrical Forum area at ElectriciansForums.net
HappyHippyDad
Supporter
Gloucestershire
Morning..
I have a garage fed by 4mm, 2 core SWA. It is a 25m run from the CU. Can I use the armour as the CPC? The Main house is TT.
I have always used 3 core so have not come across this before. i am about to check my notes as I know I have information on this and will find the formula to work it out but I wanted to start a thread as well in case I miss anything.
Cheers.
Apologies if I’m hijacking @happyhippydad, isn’t there a certain swa cable size that most all cables under that size would comply for use of swa armour as cpc?....
Two core, 120mm starts to become the size where Table 54G may not be complied with. The three and four cores are larger than that but without looking can't remember.
With regards that table... How can he just give a fixed 'yes' or 'no' dependant solely on the CSA of the cable (and the amount of cores)?
The table he bases it on 54G is now table 54.7 on page 198 of the BBB. That table uses the value of K1, K2 and S (assuming the CSA of the line conductor is <16mm as in my example). All of these are variables not constants so you cant give fixed values based solely on CSA of the conductors of the SWA.
For example... K1 and K2 vary depending on the cable being thermoplastic or theromosetting and even more of a variable is S as this depends on I and t??
Edit... I've read the tables a little more now and see there are different tables for thermoplastic/thermosetting etc so that just leaves S?
S is the CSA of the line conductor so is the value you are using as the basis for the selection of the CPC.
I think originally 3c swa was really only meant for 3 phase machines etc
If you just required line and neutral you used 2c swa
I think once swa started being used more domestically it all changed and home electricians and DIYer s would use 3c because they could connect line neutral and earth using cores and not having to use the armour as an earth
Reply to Can I use the sheath of the SWA as the CPC in this example? in the UK Electrical Forum area at ElectriciansForums.net
totally agree
You would treat it as a TT installation.