HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,295
Reaction score
6,535
Location
Gloucestershire
Morning..

I have a garage fed by 4mm, 2 core SWA. It is a 25m run from the CU. Can I use the armour as the CPC? The Main house is TT.

I have always used 3 core so have not come across this before. i am about to check my notes as I know I have information on this and will find the formula to work it out but I wanted to start a thread as well in case I miss anything.

Cheers.
 
Apologies if I’m hijacking @happyhippydad, isn’t there a certain swa cable size that most all cables under that size would comply for use of swa armour as cpc?....
Two core, 120mm starts to become the size where Table 54G may not be complied with. The three and four cores are larger than that but without looking can't remember.
 
With regards that table... How can he just give a fixed 'yes' or 'no' dependant solely on the CSA of the cable (and the amount of cores)?

The table he bases it on 54G is now table 54.7 on page 198 of the BBB. That table uses the value of K1, K2 and S (assuming the CSA of the line conductor is <16mm as in my example). All of these are variables not constants so you cant give fixed values based solely on CSA of the conductors of the SWA.

For example... K1 and K2 vary depending on the cable being thermoplastic or theromosetting and even more of a variable is S as this depends on I and t??

Edit... I've read the tables a little more now and see there are different tables for thermoplastic/thermosetting etc so that just leaves S?

S is the CSA of the line conductor so is the value you are using as the basis for the selection of the CPC.
 
I think originally 3c swa was really only meant for 3 phase machines etc

If you just required line and neutral you used 2c swa

I think once swa started being used more domestically it all changed and home electricians and DIYer s would use 3c because they could connect line neutral and earth using cores and not having to use the armour as an earth
 

Reply to Can I use the sheath of the SWA as the CPC in this example? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top