Hi Due to Covid, I can't get an electrician to come out to fit a single semi flush lamp. So I am going to fit it myself.

So some advice would be very helpful - but if you live local to Stratford Upon Avon and happy to come out for a small job, please let me know.

At the moment there is a standard ceiling rose with what looks like 3 (red) loop wires.

I have looked at some online videos and they say use a Way Go connector for the loop wires - is this correct?

Fixing and assembling I can do - but I want to make sure that I am wiring the electrics properly.

I've attached some photos - is there any tips you can offer?

Thanks in advance!
 
if you have 3 reds, wago them but do not connect to light. then you will have 3 blacks. 2 will be N to light, 1 will be switched L to light. hoefully the switched L (black) will have a bit of red sleeve onit. make sure the earths are all connected and also to the light if it has provision for earths.
 

Attachments

  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Rose_9349.JPG
    350.1 KB · Views: 98
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 1-0700.jpg
    635.7 KB · Views: 104
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 2-0702.jpg
    531.5 KB · Views: 91
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 3-0701.jpg
    638.5 KB · Views: 98
Hi Due to Covid, I can't get an electrician to come out to fit a single semi flush lamp. So I am going to fit it myself.

So some advice would be very helpful - but if you live local to Stratford Upon Avon and happy to come out for a small job, please let me know.

At the moment there is a standard ceiling rose with what looks like 3 (red) loop wires.

I have looked at some online videos and they say use a Way Go connector for the loop wires - is this correct?

Fixing and assembling I can do - but I want to make sure that I am wiring the electrics properly.

I've attached some photos - is there any tips you can offer?

Thanks in advance!
 

Attachments

  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Rose_9349.JPG
    350.1 KB · Views: 87
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 1-0700.jpg
    635.7 KB · Views: 72
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 2-0702.jpg
    531.5 KB · Views: 53
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 3-0701.jpg
    638.5 KB · Views: 54
Was that earth wire already out of that terminal?

if you have 3 reds, wago them but do not connect to light. then you will have 3 blacks. 2 will be N to light, 1 will be switched L to light. hoefully the switched L (black) will have a bit of red sleeve onit. make sure the earths are all connected and also to the light if it has provision for earths.
Thanks for this. Here are the photos. There are not 3 black.
 

Attachments

  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Rose_9349.JPG
    350.1 KB · Views: 50
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 1-0700.jpg
    635.7 KB · Views: 46
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 2-0702.jpg
    531.5 KB · Views: 48
  • [ElectriciansForums.net] Can't get an electrician to come out for a small job!  So help needed!
    Light 3-0701.jpg
    638.5 KB · Views: 100
You have two reds and two blacks, one of the blacks has a red sleeve.
The one with the red sleeve on should be the switched live to the light (to brown). The black with no sleeve should be the neutral to the light (to blues) the remaining two reds to go into a two way wago. As the light fitting is double insulated/class2 the two earths (cpc's) can also go into a two way wago. Ensure all cables are pulled into the new fitting with no wires exposed in the ceiling void.
I do however suggest you employ an electrician to ensure correct polarity
 
Last edited by a moderator:
You have two reds and two blacks, one of the blacks has a red sleeve.
The one with the red sleeve on should be the switched live to the light (to brown). The black with no sleeve should be the neutral to the light (to blues) the remaining two reds to go into a two way wago. As the light fitting is double insulated/class2 the two earths (cpc's) can also go into a two way wago. Ensure all cables are pulled into the new fitting with no wires exposed in the ceiling void.
I do however suggest you employ an electrician to ensure correct polarity
Thanks, that is very helpful. Now I see that I do have two blacks (one disguised as red!). Do I push the two reds with wago and the two earths with wago into the ceiling void (making sure there are no exposed wires). So there will only be two wires (black and black with red sleeve) pulled through to the new light terminal. I have posted the job on mybuilder - but I think it is too small a job so had no responses yet!
 

Reply to Can't get an electrician to come out for a small job! So help needed! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
570
I am starting out as an electrician in Merseyside and have recently obtained my first ECS card. I have trained with an online colllege for the...
Replies
0
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top